New boiler install...Christmas came early.

Options
IMG_9765.JPG IMG_9771.JPG IMG_9772.JPG

How'd I do? Certainly feels like an upgrade over the 2-3x oversized Penco. Ended up with the EG40. It's been running for over an hour with no pressure in sight, so I'm looking forward to that. Oddly it overheated our master bedroom which was typically a cooler room by design with a size 4 vent. I'm going to give it a couple cycles to settle in and looking forward to see how the run cycles compare this weekend as we approach single digits. NE Steamworks backup their reputation. Thanks for everyone's advice!

EdTheHeaterManWaherdennis53

Comments

  • delcrossv
    delcrossv Posts: 2,204

    Ooooooohhh! A very Merry Christmas indeed!

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • LRCCBJ
    LRCCBJ Posts: 1,043

    Very well done. That is a beautiful install.

    Like 6 other folks on the forum, I will not be surprised if you make NO PRESSURE with the huge risers and a terrific drop header. An unexplainable phenomenon…………..no pressure if you do a drop header!!

    My take:

    The resulting exceedingly dry steam results in the radiators having MORE capability than the calculated EDR.

    PROVEN at least seven times with NO EXPLANATION!!

    delcrossvWaher
  • jesmed1
    jesmed1 Posts: 1,563
    edited December 2024

    I only know what crappy steam boiler piping looks like, because that's what usually gets posted here by owners with problems.

    But I know just enough to know that is a work of art!

    EdTheHeaterManWaherRTW
  • TKPK
    TKPK Posts: 74

    looks like a dream

  • delcrossv
    delcrossv Posts: 2,204

    "Oddly it overheated our master bedroom which was typically a cooler room by design with a size 4 vent"

    Probably due to better steam flow.

    Pop a Vent Rite on to tame that bedroom rad.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • I really like it. I just think you need to get the insulation back on that near boiler piping. Here is an idea to make it really festive. On Festivus for the rest of us

    Untitled Image

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    delcrossvRTWGGrossjesmed1
  • ethicalpaul
    ethicalpaul Posts: 8,993

    those king valves are wild

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    delcrossvEdTheHeaterManWaher
  • Kjmass1
    Kjmass1 Posts: 294
    IMG_9775.png

    looks like it settled in after the initial run (yellow line).

    delcrossv
  • Beautiful install! NE Steamworks services my boiler and they are an outstanding crew! When it comes time for my boiler and its janky piping to be replaced, if I can't gather the courage to do it myself they are the only ones I will let do it!

  • jesmed1
    jesmed1 Posts: 1,563

    I love that beestat app! (You know you are a geek when…)

  • So pretty! Got that new boiler smell. 🤣

    Lifelong Michigander

    -Willie

    delcrossv
  • Kjmass1
    Kjmass1 Posts: 294

    Same, it’s great. It’s going to be super cold Monday, so looking forward to seeing how it compares with runtimes.

  • Kjmass1
    Kjmass1 Posts: 294

    I’m a bit surprised how long it takes to get to the end of main vents. The risers off the boiler are scorching within a minute or two, but takes almost 7+ minutes to get steam out of the drop header and up in to the old piping. Then almost 15 minutes to get to the end of the main with 2x #2 air eliminators on a semi cold start. Boiler is half the size though.

  • LRCCBJ
    LRCCBJ Posts: 1,043

    Yes, that makes no sense. If the piping is "warm…………..say 130F"………it takes about 2.5 minutes to reach the end of a 2.5" main………….about 60'…………with a 260K boiler, IF you have decent venting (TWO Gordon #2) in the extension of the main (aka dry return).

  • Kjmass1
    Kjmass1 Posts: 294

    It was 3 hours since the last cycle so I guess technically a cold start.

    Sat there with a timer and it took 7 minutes for the 90 where it ties in to old mains to get hot hot.

    Going to be 9F on Monday so should have some better run cycle times.

  • delcrossv
    delcrossv Posts: 2,204
    edited December 2024

    Significantly smaller boiler and a lot more metal near the boiler all radiating nicely. Insulate the near boiler piping and you'll see major improvement. 👍

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Kjmass1
    Kjmass1 Posts: 294

    2 things someone else mentioned about this install:


    The top of the wye for the Hartford loop sits at 3” below the waterline. Manual says 2”.

    Manual also says EG-40 should go 2” riser to 2.5” header, this was installed as 2” to 2”.

    I don’t want any warranty concerns. Are those recommendations, or requirements? Should I address with installer?

  • What’s the height of the Hartford loop, it looks very low, obviously hard to tell from the pictures but it seems well below the water line

    Also why the valves on the header, not a critique or anything I’ve just never seen that before

  • delcrossv
    delcrossv Posts: 2,204

    "King" valves to close off system for boiler blowdown. Nice!

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    tcassano87
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 20,938

    Not to critique things but they set the boiler where they did to line up the flue. I think I would have turned the boiler 90 degrees to the left so the controls would not be up against the water heater.

    ethicalpauldelcrossv
  • Kjmass1
    Kjmass1 Posts: 294

    I didn’t realize how much piping would be coming off the right side, we are planning to wall off the room at some point, so I had them move it over just a little bit. In hindsight probably would have had them done it differently.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 20,938

    @Kjmass1

    Not a deal breaker. Just wondered why with all the room.

    If you wall it off make sure to allow for combustion air for the boiler somehow.