HOT WATER BASEBOARDS, Stumped

stagerock
stagerock Member Posts: 4
edited December 2024 in Oil Heating

Some info…. The return on the 2nd floor is always warm even when heat is off, the return on the 1st floor is cold when heat is off. (1st floor is in or under a slab) The interesting part is that every once in a while the heat on the 2nd floor skyrockets to 80 degrees even when the thermostat is off. I have only noticed this when it gets warmer outside. This has happened 3 or 4 times in 2 months. Other than that, this 12 year old system has worked perfectly with no issues. Any thoughts?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,143

    Are those Green Taco circs I.F.Cs?

    GGrossSuperTech
  • Intplm.
    Intplm. Member Posts: 2,633

    Seems to be a typical flow-control valve issue. If not in those circulators you will need to install some.

    stagerock
  • stagerock
    stagerock Member Posts: 4

    They are green Taco circulators. Both were replaced last season.

  • stagerock
    stagerock Member Posts: 4
    edited December 2024

    If not in the circulators. Why would this issue appear after 12 years?

    Couple more pics of the backside of the system.

  • Grallert
    Grallert Member Posts: 962

    It's likely that the original pumps had flowckecks in them. The new pumps probably don't

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

    stagerockSuperTechIntplm.
  • stagerock
    stagerock Member Posts: 4
    edited December 2024

    Thank you everyone! Flow Checks are missing in the circulators that were replaced.

    Installed: Taco 007-F5 > I need: Taco 007-F5-7IFC
  • SteveSan
    SteveSan Member Posts: 284

    If the date codes on the 007-F5 are after 2003, then the discharge flange should accept an IFC. The part# for the IFC would be 0010-025RP. No need to purchase a complete pump with the IFC.

    Hope this helps.

    If you have any questions, please give Taco Technical Services a call during normal business hours Mon-Fri 8am-5pm EST 401-942-8000 and just ask for Technical Services.

    GrallertSuperTechstagerock