One pipe steam system issue

Hi newbie here!

Hope everyone is doing well. I have a one pipe steam system and all the radiator are getting hot except for one.

The pipe leading up to the system is cool half way to the system.

Things I have done:

  1. Changed the air valve
  2. Changed the pitch pitch of the pipe
  3. Change the pitch of the radiator.

All with similar results.

Any troubleshooting advice is greatly appreciated! Thanks in advance

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,950

    The pipe leading up to the system is cool half way to the system.

    What do you mean by "system" here?

    The problem is likely a pitch issue with the pipe for that radiator holding back the steam

    Does it eventually get hot on a very long call for heat? Do you ever hear any gurgling from that radiator?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,780

    It's possible that the disk in the supply valve is broken and blocking the flow of water and steam.

    You could have a bad air vent. You could remove the air vent and install a 1/8" IPS pet cock or ball valve in the vents place temporally. See if the rad heats with the vent removed and the valve open.

    Don't get rusty water on the curtains or the floor.

    Grallert
  • aiostellar
    aiostellar Member Posts: 3

    Thanks for the quick response. Pipe leading up to the radiator. Did a very long call for heat and still nothing.

  • aiostellar
    aiostellar Member Posts: 3
    edited December 2024

    Thanks for the quick response.

    Check the supply valve and its not broken.

    Changed the air vent with 2 different ones and same issue. Also, removed the vent with the valve opened similar results.

  • ethicalpaul
    ethicalpaul Member Posts: 6,950

    that is odd. The next thing I would try would be to close the valves on many of the other radiators and try a long call for heat

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • dabrakeman
    dabrakeman Member Posts: 653

    Is this a new problem? Can you show us pictures of the radiator and of the supply pipe in the basement?

  • BobC
    BobC Member Posts: 5,508

    You may have a main vent that has failed or the system is not producing enough steam.

    How is the boiler fired? If it's gas fired you may not be getting enough gas at the boiler. Several years ago ,y system did not seem to be working right and after hearong some neighbors complaining I checked my gas pressure and found it was dropping to just over 2PSI under load. The gas company replaced the incoming gas line (the 80 year old pipe was filled with rust, and the pressure was fine after that.

    Clock the gas meter and make sure it's burning gas at the correct rate -

    "Look for the smallest test dial on the meter. Get a stop watch. Get the single piece of equipment you want to clock running. Everything else should be shut off, don't worry about pilots on other equipment. If for instance the test dial you are using is the 1/2 foot dial let it make two rotations (makes the math easier) It becomes the same as a 1 foot dial. So lets say it took 20 seconds to make two rotations of the half foot dial. You divide 20 into 3600 (number of seconds in an hour). In this case 20 divided into 3600 is 180, what is 180 it is 180 cubic feet to then find BTU's multiply 180 times the Heat Value of a cubic foot of gas in your area or if you don't know use 1,000 which means the equipment you clocked is burning 180,000 BTU's per hour. This should closely match what is on the rating plate of the equipment listed as INPUT.There are charts and tables for all of this in NFPA 54 National Fuel Gas Code. There is also a procedure for altitudes in NFPA 54."

    Bob

    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge