Efficiency of an indirect water heater
Comments
-
With respect to all the talented techs on this site who love putting together indirects, there are so many negatives that no homeowner should ever want to allow one in their house.
- Boiler has to run all year, heating your house in the summer adding to cooling cost
- Added piping labor
- Added circulator cost to buy and run and fail
- Added heat exchanger cost
- When the boiler fails you lose heat and hot water
The argument used to go, I think, that electric resistance heating is expensive, but that was never really an issue. The cost of even electric resistance water heating is very cheap, check the energy guide on the electric water heaters.
But now with the existence of heat pump water heaters, even that weak positive has evaporated.
All I can think is that heating techs just love putting together the fun pieces of an indirect with pipes while convincing themselves incorrectly that it is saving money somehow for the homeowner despite all the additional costs and maintenance. Look I get it, I have done tons of unnecessary fun things in my basement with my system, but that's because it's my system and I like to mess with it. Your normal homeowner doesn't have that reason.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
The only reason I have an indirect is because I picked up a used electric tank for $50 and put a plate heat exchanger with a cheap recirc pump on it for a simple DIY one.
I would have never bought a real indirect. Even with free labor just BOM cost plus all the bits is simply not worth it.
Unfortunately up here in the great white north the cost of a HPWH is silly, so I have to settle for running my DIY unit.
Like anything hydronic, they are fun to play with though :)
1 -
@Kaos said:
"I would have never bought a real indirect. Even with free labor just BOM cost plus all the bits is simply not worth it."
OK, so my beef with our atmospheric natural gas water heater is that it's sucking heated building air up the chimney 24/7. I thought an indirect would be the logical next step to eliminate that when we replace a boiler and could plumb in an indirect.
I know the tanks are expensive. But so is an HPWH. Would we be better off switching to an HPWH? That won't last as long as an indirect, and it will be a cold-air source in the basement, which is already cold in winter, which is the problem I'm trying to solve. Because this is a 4-unit condo building with the washer and dryer in the basement, so all the owners use the basement for laundry. So wouldn't an indirect make more sense in this case?
0 -
there is no one correct answer to DHW production. Even the option that makes the most sense today , could change based on energy cost and availability.
maybe future water treatment chemicals pinhole certain tanks quickly?
Maybe the AI computer farms suck all the juice from the wires🤔
Who knows?
Ive been happy with solar thermal providing probably 50% or more of my needs since the 1970’s. Very little out of pocket for materials, and my own labor helps the roi
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
In cold climates, indirect tanks are a great option with a high efficiency boiler for lifetime costs to operate, they are often used to upgrade from electric tanks and tankless coil boilers that do not produce enough hot water, and the source energy use is less than electricity from the grid so they are better environmentally. And they deliver nearly endless hot water, which we Americans love.
As @EBEBRATT-Ed noted, heat pump water heaters are nascent technology and they operate like putting a small AC unit inside your house. They are more disposable than repairable, and the output is about 1/4 of the output of an electric tank (unless they switch to electric resistive backup, which defeats the purpose). This means it would take about 15 to 25 HPWHs running in parallel to equal the output of a single boiler (the storage capacity makes 40 to 60 gallons first hour draw possible, which does work for specific applications). When comparing DOE energy use for hot water it would cost about $1500/yr for electric tank hot water (0.95 UEF) and about $450 for natural gas or oil (75% hot water efficiency) for the most recent EIA New England residential energy prices of about $0.30/kWh here and $2.40/therm here (that difference is $12,600 in a 12 year life, most indirect tanks last much longer). The HPWH cost will be less to operate in the summer where it helps with AC, but it will add to heating costs in the winter (and it will run on electric backup at times), so it will cost more to operate than the indirect tank and take several hours to recover.
Where do HPWHs make sense in cold climate? If a rebate makes them effectively free, go for it.
President
Energy Kinetics, Inc.1 -
You can always get a power vented water heater. These have significantly smaller stack losses. There are even some models that have a fresh air intake so they don't use building air for combustion.
Around me, the norm for smaller multiplex is either one large natural gas water heater or a bunch of resistance tanks, one for each unit. Ie triplex with a boiler:
Resistance tanks will last a long time if you change the anode once in a blue moon. My repurposed resistance tank is 22 years old and on its 3rd anode.
1 -
Hi ethicalpaul -
Sorry to hear that you have had such poor experiences with Indirectly heated domestic hot water. By contrast, we have had very positive results with our Indirect, heating our Domestic Hot Water. It has run very reliably for over 15 years at over 90% thermal-efficiency, saving us lots of money compared to the alternatives.
Our boiler does not have to "run all year", because our Indirect only runs to DHW Demand, which is about 8 minutes every 2 hours. This does not "heat the house" because the Indirect jacket heating system and the building space heating systems are separate - no heat moves between the two.
The Supply and Return Heating Piping between the boiler and Indirect is short and simple. The pump is an ECM Circulator which runs reliably at very low power consumption. Water quality is key to long, reliable pump life.
Why do you need a Heat Exchanger ? The Indirect tank is already a heat exchanger. Adding an extra Heat Exchanger just complicates the system and reduces efficiency.
Yes - When the boiler fails you would lose both building heat and domestic hot water. This is a bigger problem, which is Not the Indirects fault ! We have run 26 years since Day One without a boiler failure, so I do not quite understand why this is such a concern to you. Why does your boiler fail so often that this is a concern ? Do you have water quality issues ?
Our experience with an Indirect for domestic hot water has been a huge success by all measures, including high efficiency, high reliability and low operating cost - I would not do it any other way !
Doug
3 -
I'm glad you like it, but if I am guilty of being too pessimistic, I think you are a little too optimistic :)
I'm not sure how you can say your boiler doesn't run all year when you say it runs 8 minutes every two hours. The boiler is losing heat 24/7, to me that is waste.
Can you explain how the boiler isn't in your building space? Do you keep it in the barn? Thanks!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
OK, thanks. I have looked at the power vents, but we don't have any good place to do sidewall venting. I don't think we could afford 4 separate resistance heaters, but maybe we could get away with 2 large ones for 4 units. Electricity is going to be more expensive than natural gas here in the Boston area, so then I have to do the math to figure out whether we'd really save anything.
0 -
@ethicalpaul come on, your statements lead me to believe that you have never been in a home with an indirect tank and the only ones you have seen are in pictures on here. Most of the homes in my area have indirect water heaters, I work on them all year long and I have never been in a basement that I felt was any warmer as a result of the indirect water heater being heated. Nevermind it "heating up the entire house". People prefer them because they are reliable, last a lot longer than typical tank or tankless water heaters and they never complain about running out of hot water. Maintenance? What, replacing an anode rod every few years? That's nothing compared to the maintenance a combi needs or a tankless water heater needs.
I've lived with a tankless coil boiler, electric water heater and an indirect water heater. By far the indirect water heater has been the best.
0 -
I'm sure it works great. I'm not sure how you could tell how much it was heating the house during the summer from the basement, but OK.
You put quotes around "heating up the entire house" as if I said that, but I said "Boiler has to run all year, heating your house in the summer adding to cooling cost"
I really don't like it when people say I said things I didn't say. It happens a lot on this forum for some reason.
Less maintenance than a combi or tankless water heater, that's great, but I don't think that's saying very much. How much compared to an electric water heater?
Anyway, I was pretty clear what I didn't like about them, it's up to every individual to decide if I'm making any sense. Thanks for the reply, though.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
@ethicalpaul are you implying that every other water heater doesn't also have standby losses to the space? Strange hill to stand on.
1 -
-
@Doug_7 "15 years at over 90% thermal-efficiency"
I have seen these 90%+ efficiency bandied about for indirect, I'm curious where it comes from?
Based on my observation, the best you can get is mid 80s in the winter and about mid 70s in the summer. And that is with a high efficiency modcon with proper setup.
If somebody has test data for an indirect showing seasonal energy use, would definitely be interested to see it.
0 -
Better yet, you show us the data showing any mod/con under any circumstances performing at under 85%. Unless everybody else's combustion analyzer and calculator are broken, 90+% is almost always the case.
0 -
-
No, but in addition to the standby losses of the tank, an indirect also has all the standby losses of the boiler, which must be re-heated in order to put heat into the tank. Surely someone before me must have thought of this negative aspect.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
there are different efficiencies at play here. The boilers combustion efficiency, shown on an analyzer, then the heat transfer efficiency, then the tank itself, mostly shell loss.
From a pure water to water heat transfer nothing beats, or comes close to a plate heat exchanger which can run in the 90% range. The surface area, shape of the plates and the counter flow fluid all contribute. There is no possible 100% energy transfer.
With a plate HX getting into the 90 plus range starts to cost some pumping power however, to push high velocity through all the patterned plates.
The term the plate HX industry tends to use is effectiveness instead of efficiency and the software usually includes that %
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Not all Heat Losses are equally bad. Some are large and significant. Some are trivial. It is vitally important to know the difference. This is why we need to measure and quantify the heat losses and respect the facts as shown by the data. Otherwise we are chasing down every rabbit-hole.
ModCon Boilers are designed to minimize jacket heat losses. My ModCon Boiler is in a sealed boiler room. The heat losses from my boiler are trivial, especially when running only 8 minutes every 2 hours. My boiler definitely does not "heat my house" in the summer. But the boiler heat losses are included in the boiler thermal efficiency.
I know a plate heat exchanger is good, primarily because of the small size and large surface area - but why do you need one in the first place ? Adding an extra Heat Exchanger just complicates the system, increases the ∆T and reduces efficiency. I prefer to use an Indirect type that does not need an external heat exchange - because it has an internal heat exchanger which will always be more efficient.
My Indirect is a Smart stainless-steel jacketed tank-in-tank type with a very large heat transfer area. It is a very-efficient heat exchanger. This large heat transfer area allows the Boiler to run at a lower ∆T and higher efficiency when making DHW. No external plate heat exchanger required.
Equipment selection and system design make the difference on system efficiency and reliability. This forum should really be discussing "Best Indirect DHW System Design".
1 -
You have to be careful with the use of efficiency here. Us nerds care about temperature efficiency, what most people care about is thermal efficiency. X$ of fuel gets me Y gallons of hot water.
A plate heat exchanger, or coil inside an indirect is pretty much 100% thermal efficient. Any BTU lost from the boiler loop is transferred to the hot water tank.
The temperature efficiency just means the boiler needs to make slightly hotter water to transfer this heat. In case of a heat pump this temperature efficiency actually matters as making hotter water costs you COP. With a modcon, there is a small effect but not enough to matter.
So overall efficiency of a modcon connected indirect is only burner efficiency, piping losses, jacket losses and heat loss from stored heat in the boiler and pipes at the end of each cycle. And that number is somewhere between 75 to 85% with a good setup.
0 -
Thanks I will say that when I am thinking about the most heinous indirect setups, they are typically with oil burner boilers that are not very efficient and are hulking masses of iron with poor insulation.
Mod-cons have their own concerns of course of (lack of) longevity and maintenance but their efficiency is apparently pretty good.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
@ethicalpaul said:
"when I am thinking about the most heinous indirect setups, they are typically with oil burner boilers that are not very efficient and are hulking masses of iron with poor insulation."
Which brings us right back to the Energy Kinetics bar chart I posted upthread, showing a range of overall system efficiencies from the low 60%'s for a cast iron boiler with indirect up to the high 80%'s for an EK low mass steel boiler with indirect.
So an EK-type low mass boiler with an indirect apparently can reach the "non-heinous" range. I think Roger would say that one of the clever features of the EK controller is that the standby losses of the boiler you're referring to are partially recovered by post-purging into the indirect tank, which is one factor in getting that 85% system efficiency he advertises for the System 2000.
3 -
It depends on the boiler. An old boiler that has a large water volume is a lot different than the modern three pass or even the wet base pin type boilers. Something like my WBV-03 doesn't run long enough when heating the indirect water heater to make any noticeable difference in temperature in the basement.
As far as maintenance versus an electric water heater, it's definitely less. My indirect doesn't even have an anode rod, so the only maintenance is flushing it once a year and replacing the scale stopper cartridge I installed. My electric water heater needed anode rod replacements, flushing and I had to replace the elements once. It would run out of water if back to back showers were taken. My 41 gallon indirect never runs outs, no matter how much demand is put on it.
0 -
Recovery is why we do it. With a well designed system and basic hydronic maintenance they last. Reliable comfort and convenience makes a lot go round.
Standby losses of a good indirect / Bad case vs good? Maybe 32k btu to 8k btu per day. 60 to 20 cents a day in my market. What ever it is, I'm just trying to get a sense of scale here.
Fuel converted to stored heat/ A good indirect and modcon might be 14% less efficient than the best tankless. But the tub fills fast!
Daily hot water of 80 gallons @ 70F temp rise is 46,648 btu half a therm or so. A tankless wins by maybe 6,500 btu saved or 17 cents. So we add standby and fuel conversion saving and get 77 cents a day saved for the bad case and 37 cents for the good case.
$280 or $135 a year savings. To get that savings you spent what to service the tankless? I wounder how much more or less energy and resources it took to build a tankless and the bigger gas line and flue, etc. vs the indirect and it's stuff? That's the hub bub? Carbon or Money? Or is this a design elegance thing? Maybe it's a sales pitch vs sales pitch thing. .
2 -
I certainly never suggested a tankless
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
it in not possible for a coil in still water to be more efficient than a heat exchanger with two moving flows under turbulent conditions
With the flat plate design software we can determine actual performance, effectiveness under any flow and temperature condition, even put in a fouling condition
With a tank that would be a very complicated calculation as the water is at different temperature from top to bottom, so the heat exchange rate is different through the thermocline
I have never seen and performance rating on an indirect, other than a simple heat loss per hour number
Bock water heater company made the Caleffi solar tanks single and dual coil. I visited their lab to watch some testing
we wanted to determine how much energt could be pulled out of the top cool for radiant heat. If I dig deep I can find t report they generated from various flow conditions. It wasn’t great, even with the massive 1-1/2” coils we used
Page through this journal to see how crazy the math gets
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
look inside a typical boiler to get an idea why 100% heat transfer is not possible
In this example the water does not get to the flame temperature or even close to the wall temperature. With or without the micro bubbles😉There are efficiency losses at every step of the heat transfer
Although the micro bubbles do hamper the heat exchange
Kaos, show me an indirect that can produce 180 tank temperature with 180 SWT. If you have one, it would be worth a lot of money!
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
The cheapo steel tank HP's look like what, when viewing them with a cradle to grave lens and real world failure numbers? Looks like environmental crypto currency or clean coal. Granted a resistance tank is cheap and if it can do the job, then it's a good option. Swapping them bigger tanks out more frequently with higher energy cost adds up. Is it really a win? In my market 46,648 btu by resistance heat is near $5.04 a day. While natural gas would be near half that. Use patterns existing hardware and water quality are factors. Simplified judgement of indirect heaters isn't conclusive and universal truth. If we were all desperately trying to make it on time to the tipping point ferry then every lbs of carbon saved counts but It sure doesn't look like we are going to make that boat. Is that a means of heating water issue or something a bit deeper? Problems, problems, beware of the solutions.
0 -
Do not confuse "efficiency" with "heat transfer rate" and the measures used ti increase heat transfer rate.
Efficiency is "Heat Out divided by Heat In". A coil in still water will almost always be more "efficient" than a heat exchanger with two moving flows under turbulent conditions. A coil in still water can be 100% efficient if there are no external heat losses. It is just kind of slow, so people try to speed that up, and sometimes confuse that with "efficiency".
A heat exchanger with two moving flows under turbulent conditions will speed up the heat transfer rate,, but that does not make it more "efficient". As an external device, your heat exchanger has heat losses. That is why it is insulated - to reduce those heat losses.
The heat loss per hour of an Indirect is a measure of the standby heat losses. It is pretty low.
Heat losses can be measured, added up and subtracted from 100% to determine "efficiency".
I do not use an Indirect that heats a coil in still water. I do use an Indirect that is a jacketed stainless steel tank-in-tank with a very large heat transfer area. As you increase the heat transfer surface area you can reduce the ∆ T. The very large heat transfer area allows me to run quite low 130º F boiler water temperatures, further enhancing boiler "efficiency".
What boiler water temperatures do you use with a flat plate heater ? A large flat plate heater can use a lower boiler water temperatures, allowing higher boiler "efficiency" - but there is a cost trade-off.
1 -
i would consider an indirect to be more like a shell and tube HX design.
As such the companies that build both types seem to have the best actual data. I would say AlfaLavel is one of the largest Hx manufacturers, here us their take.
About the best transfer tank I tank seen is the TurboMax, which us a tank crammed full of copper hx tube. But still with one moving fluid the transfer will be limited
Id still put my money on the EK external plate hx.
Very easy to insulate a plate Hx, manufacturers offer the foam shells to tightly fit.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Hi
hot_rod
-I agree that an Indirect that uses internal coils for heating, is like a shell and tube HX design. The problem is that you just can't pack enough tubes into one to make it fast and efficient. I would not use such an Indirect design for this reason, TurboMax or not.
An Indirect that is a jacketed stainless steel tank-in-tank is nothing like a shell and tube HX design. No Tubes - No comparison. The heat exchange all happens inside the Indirect DHW Tank without any internal tubes or coils. Very simple, because the heat exchange all happens inside the DHW Tank where there are no heat losses to the outside. Very efficient.
All Indirects ar not created equal. The Triangle Tube Smart Stainless-steel tank-in-tank Indirects provide more efficient heat transfer in the Indirect, and the large heat transfer surface reduces the ∆ T on the boiler, further increasing boiler efficiency.
An Indirect that is a storage tank with an external plate heat exchanger cannot be more thermally-efficient than a tank-in-tank Indirect, because the heating transfer takes place outside the Indirect where it is subject to heat losses, and they typically are designed for much higher boiler temperatures like 160º F..
Reduse temperatures, improve thermal efficiency, and save money. The cost savings really do add-up over the years.
Doug
0 -
Im familiar with tank in tank design, owned several including the older HL horizontal style. You are limited in HX surface by the tank size. plate hx can have any number of plates added to get within 1 degree. Can you show me a tank ln tank with a 1 degree approach temperature ? With flow only in the space between the tanks?
But if you are not recirculating the dhw you still have only one moving flow. Whereas the plate has two moving streams and counter flow
A good example of this is to take a look at a plate HX performance difference between parallel and counterflow
The Idronics I attached above has the numbers and examples if various HX designs
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Temperature efficiency of the heat exchanger doesn't matter here. If the approach temp is 10F or 1F, the only thing it changes is how hot the SWT and RWT will be. That has a very small effect on boiler burner efficiency and no effect on the rest. An indirect with 95% or one with 90% temperature efficiency has the exact same thermal efficiency.
As for temperature efficiency, even an indirect with the lowest temp delta will eventually have some scale buildup and this will make a much bigger difference. My DIY indirect used to have a coil inside the tank, after a couple of years I lost about 1/2 the recovery because of scale buildup. The reason I went with the plate HX is that it can be easily cleaned.
In my case the thermal efficiency of the indirect did not change because of the increased approach temp. The only thing that happened is max BTU/h it can absorb decreased so recovery took longer (boiler was running at 1/2 output but 2x as long).
0 -
The approach temperature tell you how much heat was exchanged between the two flows
My question is have you seen a coil or tank in tank indirect run a 1 degree approach?
The topic is the efficiency of the tanks heat exchange. Doesn’t matter what is suppling the A side. Could be a 40% wood furnace or a nuclear reactor😉
Im looking at how well the exchange in the tank, or outside the tank is
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If you are looking for temperature efficiency, you can back calculate from the spec sheet. ie:
These usually list continuous output which is what you want to use. They also have the surface area so if you do the heat exchanger math with delTm, you can figure out the flow rates and temp rises you can get at other points.
0 -
hot_rod - Your question is "Have I seen have seen a coil or tank in tank indirect run a 1 degree approach?"
The answer is YES - at the end of every re-heating-cycle, the approach temperature is 0º F - indicating that all of the heat that can be transferred from the boiler water to the Domestic Hot water has been transferred. This is a batch-process not a continuous one. Where you end up is important and tells the tale on efficiency.
The topic is the efficiency of the tanks heat exchange. How much heat is wasted. The Smart Indirect has 40 sq ft of heat transfer area. This large surface area is useful to transfer the heat rapidly. Where you end the heating cycle is important.
Don't get mesmerized by a low approach temperature - that just means the plate heat exchanger is big - not that it is efficient. What boiler water temperature are you running into your plate heat exchanger ? Important to press all the real high-efficiency buttons and ignore the hypothetical ones, if you want to achieve maximum efficiency.
As for scaling - we are not seeing any after 15 years. The re-heat time is still 8 minutes. Smart Indirect has a unique anti-scaling design. I do not like Indirects with a coil. How often to you clean a flat plate heat exchanger ?
Doug
0 -
Let use a tank in tank indirect for an example
A TT Smart 60 has 24 sq ft of surface area for HX, from their output sheet:
180 SWT, DHW rise 90° so 50- 140°F on the domestic side
With a 100,000 btu input boiler they show 135 gph continuous AKA 2.0833333 gpm
It doesn't show the ∆T on the boiler side, lets assume 20° 180 SWT, 160 RWT
Using the SWEP HX sizing program
Putting a 10 gpm flow boiler side 100,000 btu/hr. 180SWT, 160 RWT, 90° rise on the dhw sid
I need a 3X8-26 plate HX with 3.10 sq. ft of surface area, 78% oversurfacing, accounts for potential fouling
I get 2.237 gpm on the dhw side
I think a 3x8 is about the size of the HX in most combis, the dimension of a cell phone.
So a tank in tank indirect, under continuous flow, flow moving in and outside the tank I assume? needs 24 sq. ft of surface.
A plate HX does the same job with 3 sq ft.
A clear indication of the difference in performance, the more efficient transfer of a counter flow plate HX.
Yes the boiler side cost me 10 gpm at 2.78 psi drop. Within the range of a small 15-58 size circ.
When you observe how an indirect actually works, with a cold tank temperature the exchange happens quickly, as you get closer to setpoint, the heat exchange slows to a crawl. You've lost your ∆T leverage to exchange. So the recovery time needs to be considered.
The plate gives you that 2.2 gpm as long as the boiler is fired.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@jesmed1 unless a lot of work has been done to seal up the connection between the top of the foundation and the sill and the floor the air that goes up the vent is coming in there, not from the conditioned space above. That doesn't mean it doesn't increase infiltration a bit and lower the temp of the basement a bit which increases conduction losses through the floor a little, but in most structures the amount of infiltration through the sill and out through the rest of the structure is much greater than the increased infiltration from the vent for the appliances. Vent dampers are more to keep the heat in the appliance than to reduce exfiltration.
0 -
Normal Indirect operation is a series of re-heat cycles to maintain the DHW Temperature in the 120º F range.
I prefer my tank-in-tank indirect with 40 sq ft heat transfer area, and my 130º F boiler water temperature, because it is more efficient overall - saves me a lot of money every year. My Recovery Time is 8 minutes so that is not an issue. I have watched it operate for 15 years.
Equipment sizing is very important. Sometimes over-sizing certain heat transfer equipment can save a lot of money on energy-efficiency and long-term operating costs. Ever notice how much more energy-efficient a ModCon boiler is at low firing-rates than at high firing-rates ? That energy-efficiency difference is pretty large. That is because the boiler heat-exchanger is oversized for that low firing-rate. Equipment manufacturers have to make compromises. We can find the sweet-spot.
So go with your 3 sq ft flat plate heat exchanger and use 180º F boiler water to heat it if you like. I understand what you are doing, but I do not consider that to be the most-efficient way, or the lowest-cost way to operate an indirect to make DHW.
Doug
1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements