Boiler with no draft regulator
efarrenovate
efarrenovate Member Posts: 6
edited December 2024 in Oil Heating
Hi I have a question,
While doing just normal servicing, I am coming across few boilers that has no draft regulator from whoever originally installed them. They seem to be there for a few years. Should I tell the customer it needs draft regulator or just serviced it and let it remain the way it is?
Allie
  • SuperTech
    SuperTech Member Posts: 2,661
    Check the installation instructions for the boiler. Some boilers like those from Energy Kinetics don't require a draft regulator but the majority of them do.
    jringelefarrenovate
  • Intplm.
    Intplm. Member Posts: 3,018
    @efarrenovate Do the tune-up service to the boiler and check the owner's manual. (Usually found in the rafters near the boiler) and see what it says there to verify your thoughts.
    EBEBRATT-Ed Member Posts: 20,180
    Depends on the boiler. Natural draft gas boiler do not use barometric dampers they have a draft hood.
    EdTheHeaterMan Member Posts: 12,190
    I assume you are speaking of Oil Burner Tune-Ups. If you can not locate the IO Manual in the rafters, you may be able to locate them on the internet. Do you carry a tablet with internet access with you on service and maintenance calls? You should. You should always have access to the manual of any piece of equipment you work on.
    MikeAmannefarrenovateIntplm.
  • efarrenovate
    Thanks for all your information and input. I do appreciate it.