Pnuematic Controls
If any old timers or guys with experience in pneumatic controls, could send this young commercial heating tech some literature or manuals on Pnuematic controls I keep running into it and, I kind of understand but I’m not sure about a lot of things. Thanks books, PDFS anything thank you
Appreciate the Responses, Thanks(10/22/24(8:04)
Actually if you can find some older Honeywell/ Johnson Controls / Siemens / Landis and Gyr or really old school MCC Powers catalogs they had some basic stuff in the "engineering" sections of those. I think most of those can be found in PDF form on the interwebs.
Aside from that some basic things to understand would be spring ranges of dampers and valves. A lot of systems that I used to deal with relied on the using spring ranges of a heating or cooling valve manipulate the overall control. Heating NO open valve 3-8 PSI Cooling NC valve 8-13 PSI. The concepts of direct acting vs reverse acting.
The use of EPs and pressure regulators to drop the house or main air of a system to facilitate night setback. Reciever controllers and pilot positioners are good to review.
Some basic tools are small allen key thermostat wrench, squeeze bulb with gauge for testing and calibrating. Good analog pocket thermometer, good side cutters, hemostats for pinching lines off. Grainger should have a few kits or Kele is a good place. I'll look to see if I have any old documents floating around
Owner of Grunaire Climate Solutions. Check us out under the locate a contractor section. Located in Detroit area.
appreciate all the responses thanks
@Jalen_Jalen2006 what types of systems besides "commercial" are you working on?
vav boxes / steam to hot water heat exchangers / AHUs there's a whole lot in that category depending on where you are at/ chiller or boiler plants ?
The installation instructions for the various parts (VAV controller, relay, reset controller, etc.) make good reading as well.
For pneumatic systems Its mostly heating systems. Hot water, steam, I don’t really see any cooling or anything like that.
