What size Gas Furnace and AC do I need?
farinc55
farinc55 Member Posts: 2
I have 2 floors, one of which is a basement. Each floor is about 900 sq. feet, so 1800 total. I've read that when calculating the BTU and Tonage requirement that you only use 1/2 of the basement square footage, thus reducing the total square footage to 1350 if true. Can someone tell me what size BTU gas furnace (80%) and A/C tonnage (14 seer) I'd need for my situation? Thank you.
    pecmsg Member Posts: 7,039
    The only correct way of knowing is a ACCA Manual "J" Heat load / Loss calculation! All those calculations you read about do not take into account the local conditions, house construction infiltration etc etc.
    I do advise for A/C get heat pumps for the mild seasons and 2 stories 2 systems.
    EBEBRATT-Ed Member Posts: 20,145
    As @pecmsg said rules of thumb are not the correct way to size equipment. Every building and every location change the heat and ac load. You need a proper heat loss and heat gain calculation.
    If I was forced to take a rough guess I would say 60,000 btu on heat and 2 tons of cooling but location and building construction will dictate.
  • Hot_water_fan
    Hot_water_fan Member Posts: 2,241
    Manual J. If heat loss is low enough, a heat pump only is probably a better idea. But furnace + heat pump works too.