Vent Pipe For Boiler: How Far Into Masonry Chimney?
I apologize if this is elementary, but information online conflicts.
The chimney of concern is brick with a clay liner that I think is 9 x 13". (I can't climb anymore, so I can't measure on roof.)
Our boiler vents using 5 inch diameter 26 gauge vent pipe. (100,000 btu input, cast iron sectional, not power vented, not condensing. From about 1945.)
The existing vent pipe was 30 gauge and rusted through where it enters the masonry chimney. Also in the chimney is the vent for a water heater. It is 26 gauge 3" diameter and enters the masonry separately, a few inches above the chimney vent.
Of concern is how far the new 26 gauge pipe extends inside the liner. I've read "flush to the inside of the liner", "an inch into the liner", "to the center of the liner", "shorter than the water heater pipe" and "past the end of the water heater pipe".
Thanks For Advising,
Paul
PS: A metal liner is not possilbe at this time, but hopefully in the future.
Two appliances into the same flue is very bad practice. It may not even be permitted in your area.
OK. Having said that, the stove pipe or other appliance vent should project slightly into the flue, but not excessively. A good chimney sweep person will get it right.
Thanks Jamie Hall for your advice. I appreciate it.
Going with what you advised about 2 appliances into one flue, when it is time for a liner should I specify separate liners for each appliance? They would both still go into the same masonry chimney. (Assuming they fit)
In our city, for existing installations allowed are two into one flue if neither is power vented. They also allow one to size a vent pipe large enough for both into the masonry and then put each appliance into the larger pipe. I haven't the distance from chimney for that.
Thanks Again,
Paul
As far as @Jamie Hall 's insight is very valuable and he has many more years of experience in all types of systems. There are many occasions that a water heater with a 3" or 4" vent connector is allowed to enter the same masonry chimney as an oil or gas space heating appliance that is vented just below it. The common knowledge is that the Oil Fired appliance must enter the chimney below the Gas fired appliance. It is done all the time. When venting multiple gas appliances into a common vent, the manufacturer of the appliances offer guidelines that will specify the common pipe size that all the vent connectors will be connected to.
As for how far to insert the vent connector (26 Gauge galvanized pipe is called the connector) the end of the connector must be flush with the inner wall of the liner. And it should be sealed on the inside where it connects to the liner.
3 -
@EdTheHeaterMan , who is a much better tradesman than I ever was or will be, is right. Sort of. I know something about chimneys and venting, but don't have his level of experience or knowledge! Go with what he says.
NFPA 211 calls for the vent connector to be flush with the inner face of the flue. The junction with the flue tile must be chinked with furnace cement for a tight seal.
The connector must be removable meaning you cannot permanently cement a galvanized steel pipe into a masonry wall. You can insert one into a thimble or crock that is permanently sealed to the face of the flue then make a removeable seal btw the pipe and the thimble flush with the inner face. Better yet, reline the chimney bringing the ss liner into the room a few inches and make your connection there.
A 9"x13" TC lined flue is probably grossly oversized. When the WH alone is firing it will probably backdraft. There is a 100% chance that TC lined flue would fail a Level II inspection, which it should undergo. That would bring you back to the liner. If you sweep a liner into the room, you can manifold the WH in with the boiler connector if properly sized and the vent rise off the appliance maximized while maintaining clearances to combustibles. Putting the WH above the boiler breaching is so it has the maximum vent rise. There is a lot of argument about interference from the bigger appliance blocking the little guy. I don't see that problem because I insist on a liner with manifold or I walk. I've never done the 3" WH connector above the boiler. I always test my installations including combustion analysis and a worst case depressurization test so I know it has the best chance of working under adverse venting conditions like summer time.
2 -
And I defer to @Bob Harper on venting issues. So get your chimney inspected and perhaps have a stainless steel liner dropped into the clay liner, have it curve into the basement where you can attach to the appliance connector(s) with a properlu sized manifold. The liner will be sized to the connected appliances and may be as small as 5" diameter, so it will fit nicely in the clay tile liner.
Bottom line is that you do not want a down draft to force carbon monoxide (colorless/odorless) creeeping into your home when you are asleep. You don't want to wake up dead tomorrow!
Thank You All for helping and explaining.
After reading what each of you wrote, having a liner(s) installed will move up on our "money eaters" list.
For the immediate, temporary repair I will follow the advice that you all shared as well as possible. Sealing the 3" to the inside face of the masonry is going to be interesting, but other than that I can follow the drawing that EdTheHeaterMan was kind enough to supply. There are sleeves for the connector pipes into the masonry, as Bob Harper mentioned.
At liner time, I will insist that the contractor have a Level II inspection done, as mentioned by Bob Harper.
Thanks EdTheHeaterMan for the corbon monoxide reminder. We've always been over-minimum on CO detectors. (And smoke/fire) I worked in a big city as a police officer before detectors were common. I found too many dead people from CO poisioning. (Usually gas space heaters in the house) It scared me wise.
There are two CO detectors in the basement- one adjacent to the boiler, water heater and clothes dryer. We have two on the first floor and one on the small second floor in the sleeping area.
And, it's very important to respect the expiration date on carbon monoxide, smoke and/or fire detectors regardless if the "test" button still works.
Paul
Thanks Again everyone for helping and educating.
The new pipe will be temporary until we can get a liner and manifold professionally installed with permit. But, it may have to last through winter, depending on other $$ situations.
Out of curiosity, does the snap-lok seam on the horizontal (<1/4"/ft rise) go on top, on the side, on the bottom- or is it unimportant?
Thanks Again,
Paul
There is no standard specifying where the seam must go. For practical reasons I teach keeping the seam out of 5-7 O'clock positions on horizontal runs (less than 45 degrees from level). You must have a minimum of 3 screws per joint equidistantly spaced. Again, keep the screws out of the 5-7 positions because the acidic flue gas condensate will eat up crummy electroplated screws. Even if you use ss screws the acid will attach the thin wall of the pipe at the hole where there is no zinc plating eating the hole larger and larger until the screw falls out. I've found many screws on the floor. Even though NFPA 31 calls for the male end up, this is one time I overtly defy a standard. EVERY listed venting system uses a male-down orientation to contain the condensate. It you have to hand crimp a joint and you're worried about flow disturbance just butter the joint with furnace cement for a smooth transition into the next section.
Listed CO alarms are death alarms only. They do not protect against low level CO. Get unlisted low level CO monitors.0 -
If you all don't mind two follow-up questions, I'd certainly appreciate your comments.
A) Before the vent rusted and needed repairs, if I held a smoke source just below and outboard of the draft diverter's skirt, the smoke went straight up. This happened if the boiler was off, had just fired and after the boiler was hot and still running. (Photo is attached)
Since installing the new vent, if I hold a smoke source in the same place the smoke goes straight up when the boiler is off and at first firing of the burners (vent still cool), but when the vent warms, the smoke is drawn into the skirt & up the vent. It did both this yesterday on a no-breeze day and today on a very windy day.
Is this drawing in of smoke a good thing or a bad sign?
I don't know if this is related, but also note that the vent pipe is cooler than it was before the repairs. Surface thermometer at the top of the collector usually showed 250- 300 degrees-F before repairs & now shows 180-190-F. (Boiler burning for 15 minutes minimum)
B) I'm curious why the code that EdTheHeaterMan referenced calls for the colector(s) to be flush with the inner liner. Is it bad if they protrude into the liner, but are still sealed to the clay? (The water heater's clooector protrudes in a few inches.) Just a curiosity on my part.
Thanks For The Education! It is appreciated.
Paul
If you have decent draught the smoke should be pulled into the skirt and up the vent. That shows that the stack is venting properly. Ideally there would always be a slight draught, and the smoke would always go it, at least lazily. That may not happen with a cold stack, though.
Thank You Jamie Hall for explaining the smoke being pulled into the draft diverter's skirt.
Just to check, today I tried smoke while the nearby clothes dryer was running (exhausts outside). The smoke continued to go into the skirt, so I was happy to see that.
I'll feel best when we get a liner for the boiler & water heater instead.
Thanks Again Everyone!
Paul
I ran into the same issue and ended up getting help from Emerson Pro Services to figure it out. Their tech explained that the liner should stop just a little past the chimney thimble, not pushed all the way in. Too far and it can cause turbulence or block flue gas flow. They also checked draft readings after install, which made a difference in performance and safety.
1