The Right Pressure for Steam Heating Systems
HeatingHelp
HeatingHelp Administrator Posts: 722
edited October 2024 in THE MAIN WALL
imageThe Right Pressure for Steam Heating Systems
In this excerpt from his Dead Men’s Steam School seminar, Dan Holohan shares his knowledge about pressuretrols and the optimum pressure for steam heating systems. He talks about the difference between sensible and latent heat and why a steam heating system will work at 2 psi if you only get the air out of its way.
Read the full story here
  • CarlM
    CarlM Member Posts: 13
    The right handed screwdriver is cheaper
    EdTheHeaterMan Member Posts: 12,127
    I just mentioned this to someone on another site:
    while reminiscing about his days as an apprentice, he remembers being asked to get a pipe stretcher from the work truck. Then I remarked that you could never ask that apprentice to get you one of these after pulling that trick on him.
  • Marc_18
    Marc_18 Member Posts: 22
    My boiler is slightly oversized. All vents are sized correctly. For overnight setbacks greater than 4-5 degrees, the p’tol will hit the current setting of 1.5 oz and begin to cycle the boiler.
    Question is whether to 1) leave things alone, 2) raise the p’tol setting a bit to, say, 2 oz, 3) manually raise the thermostat in stages in the morning to reach the desired house temp without pressures going above ~1.5 oz or 4) set the overnight house temperature to be higher (undesired)?
  • bburd
    bburd Member Posts: 1,302
    edited October 2024
    That's normal operation for the circumstances, I'd leave it alone.
    Bburd
  • Waher
    Waher Member Posts: 372
    Do not raise the pressure. The pressuretrol cycling the boiler at 1.5oz is doing its job keeping the system in the proper operating pressure range.
  • Megawboiler
    Megawboiler Member Posts: 19
    Right on! My single pipe system rarely goes above 1psi. This system dates back to coal days, now gas. I recently had the rust separator/low water shutoff rebuilt and the system has been a beta test Tekmar Control site for over 20 years. No indoor thermostat, just indoor/outdoor temp sensor differential data allows the controller to calculate start times to recover from overnight shutdown periods. Go steam!!! Most local HVAC guys just give me "yah right" side eye when I describe the system to them. Western Canada.