Ed, I wanted to hijack onto this thread since I have a similar but different situation and was looking for some wiring guidance that my HVAC company is missing as they are new to HeatPumps here in NJ.
My 1960s split level house has 4 'levels' plus a basement so we have a 4 zone hydronic baseboard heat attached to a Weil Mclain CG natrual gas boiler with 4 taco 572-2 zone valves, one for each 'level' and controlled by 4 'dumb' battery powered thermostats with just a red and white wire.
For cooling we've had 2 AC units, with one going to the first two zones, and attic AC unit going to the top 2 zones. Last year when the top AC unit died we replaced it with a Goodman GSZB4 heatpump, and are going to be doing the same to the lower level AC soon.
The smart thermostats we have hooked up to the AC and Heatpump are the Honeywell TH6320WF2003/U Lyric T6 Thermostat.
Right now the T6 for our AC unit on level 2 is able to be attached to both the boiler and the AC. However, the heatpump on level 3 is only hooked up to the heatpump and as such we have a 'dumb' thermostat 3 inches above it to control the boiler. I would love to be able to, at a minimum, hook the heatpumps and the baseboard zone where they are placed to the same thermostat as was able to be done with an AC unit. Additionally, I would love to replace the two remaining dumb thermostats on level 1 and level 4 with something like the battery powered Honeywell TH6320ZW2003 T6 Pro Series Z-Wave so they can all talk together and use the heatpump when it is warm enough and otherwise use the baseboard heat.
Last year I remember reading somewhere on this forum that I would need to wire a DPDT relay in but couldn't make sense of that and was just reminded of it reading your post.
Any help would be appreciated.
One piece of the puzzle is easy, since you have zone valves. If a zone valve is open, the boiler does its thing, controlled by its aquastat (or, preferably, by its own outdoor reset if it modulates).
Now. The rest of it isn't quite so simple. You basically have four zones, any one of which at any time may be requesting either heating or cooling. You also have a boiler with four zones, and you have two heat pumps (one of them is only cooling, I understand, but I dare say that will change) on two zones which can either heat or cool. You also have the question of whether to run the heat pumps or the boiler, depending on outside temperature.
You can use any thermostat which can run a heat pump and an auxiliary heat source for the interior control, although this does not disable the heat pumps when it is too cold for them outside. The auxiliary heat command from each thermostat would go to the respective zone valve. For the heat pumps, you will need relays to isolate their controls. Zone 1 and 2 thermostats would have four relays: two, with the coils individually powered by the thermostats "heat" command and their normally open contacts paralleled to control the number 1 heat pump "heat". Two more, with coils individually powered by the thermostat "cool" command and their normally open contacts paralleled to control the number one heat pump "cool". Then a similar arrangement for the number 2 heat pump and its two thermostats.
There are other ways to do it. If you into coding, a PLC could be used but would still probably require relays (depending on the output capabilities of the PLC).
Whatever you do, document everything for the next person who has to figure it out!
This will take some special designing and your system is different from all the other systems that I have helped on. In the past I have helped design an analogue system (relays and switches) to connect the digital controls to the different components. I will take some time to digest your request and come up with something that you may be able to use. Getting your contractor to understand the logic behind the design will be another hurdle you will need to overcome. Give me some time to think on this
The basic logic is going to be something like this
- Whenever the outdoor temperature is above 80° you will use the heat pumps to cool the home.
- Whenever the outdoor temperature is between 65° and 79° you will probably not need heat or cooling
- Whenever the outdoor temperature is between 34° and 64° you will want the heat pump to do the work to heat the home
- Whenever the outdoor temperature is below 33° You want the baseboard system to heat the home.
I can build you a control system that will do that based on the heat pump having legacy controls R,G,Y,W,O,C terminals (not communicating controls 1234 or ABCD).
based on the photo of the thermostat for your heat pump thermostat, you have Legacy controls
Your zone controls use a Taco 570 series valve with 1,2,3 terminals.
Once you have the interface that connects the heat pump W (which is usually the second stage of heat, or the backup electric heat) to the boiler system at a specific outdoor temperature, then the zone valves for the matching HP thermostats will operate the boiler as usual, the thermostats that are for the heat only zones will also work on the basis of not operating above 33°. That 33° to 34° outdoor temperature set point will be adjustable just in case your system break even point is actually higher or lower that 34°. (break even point is where the outdoor temperature is causing the heat pump to operate constantly and will not be able to produce enough to maintain the indoor set point heat if the outdoor temperature drops below that point)
With this information being correct, I can start on the project.
Yours,
Mr. Ed
EDIT: one other question… what is the model number of the Heat Pump and the Air Handler you are using? You can usually find that info in the documents that came with the equipment or on the actual piece of equipment.
If you are interested in just using the toggle switch idea then you can follow the diagram from above. Reprinted here:
@NJwoods, we've created a new discussion for you here to prevent confusion.
Thanks, @EdTheHeaterMan!
Forum Moderator
Here is what I have come up with.
- The Red area is in the attic
- the Green area is outdoor.
- The Gray area is the basement.
- In the basement is a working 4 zone boiler system. I used a factory diagram to illustrate that system. There are no changes needed to make that system operate.
- The thermostat wires from the boiler zines that match the Heat Pump Thermostat zones are pictured as brown thermostat wire from the basement to the thermostat location as a Red and a White wire.
- Splice a new conductor from the boiler zone R and W wire to the air handler location. (I used the Purple and Brown of an 8 conductor thermostat wire. you can use a separate 2 conductor thermostat wire to do that)
- W from the thermostat will call for heat from the Boiler only by way of a Heat Relay located in the air handler. The W will not connect to the heat pump at all.
- This may allow both heating units to work simultaneously on some rare occasions, however there may also be some cold air blowing during defrost cycle.
- If #8. causes a comfort issue, then connect W from the heat pump to W on the air handler to bring on AUX electric heat during defrost.)
- The T675 remote bulb thermostat should be set at the lowest differential setting 3°F. and select the outdoor temperature that will best match your system. The higher the OD temperature the less Defrost cycles you will experience.
I will review this design again to see it there is a better solution. Anu comments from the HH Wallies are welcome.
This is the remote bulb thermostat to measure the outdoor temperature. You can use one for each heat pump. They get wired in or near the air handler. https://www.supplyhouse.com/Honeywell-T675A1565-Remote-bulb-Commercial-Temperature-Controller-0-F-to-100-F-20-ft-capillary-Copper-bulb-sensing-element.
Thank you so much for the help and moving this thread.
This solution seems like it makes sense to me and the issue of #8 is reasonable enough to live with.
One question/thought I have is that my heat pump does not have electric heat strips for backup/emergency heat. If I get the remote temperature controller, I see there is a setting 355 Balance Point (Compressor Lockout) and lets say I set it to 40*F, is there a way to wire my boiler up to the Aux/Emergency Heat and have this balance point call for the boiler zone heat? That might be what you are describing in #10.
The heat pump is Goodman Heat Pump GSZB403610 and Goodman Air Handler AMST36BU1400.
@NJwoods said is there a way to wire my boiler up to the Aux/Emergency Heat and have this balance point call for the boiler zone heat?
YES
On your thermostat, in the programing section, you have to select the system type. if you select heat pump with Fossil Fuel backup, the compressor will stop and the boiler will start. there will be a time lag before the radiators heat up after the compressor stops. The time lag can be as much as 15 minutes, but will be at leadt 8 minutes.
that is because the sequence of operation of the boiler is this
- heat pump reaches the point where backup heat is required. The compressor stops and W sends a signal to the zone valve in the basement.
- the Taco 570 valve motor can take as long as 90 seconds from the call for heat, until the valve is completely open and the valve end switch starts the boiler.
- The boiler pre-lighting sequence may be as long as 60 seconds with pre-purge ignitor operation, trial for ignition main valve opening and proof of flame. (if there is no proof of flame on the first try, then the pre-purge sequence starts all over again add another 60 seconds))
- Now the main flame starts to heat up the cold water inside the boiler. that cna take several minutes to get hot enough water to to radiators. (once the flame is on the water does not instantly get to 160°. There is a slow to medium time lag there.
- after all that time, you will start to get some heat from the radiators. This time lag is not always noticeable, and may not be a problem. Just be aware that it exists.
I can incorporate that into your wiring design, use the outdoor sensor feature of the thermostat and perhaps eliminate the T675A. I will need to read the thermostat specifications in detail to see if that id possible.
That's gonna be a Monday thing
It appears that the thermostat TH6320WF2003 may be able to do everything you are asking. The trouble is that when you select ISU 200 = Heat Pump, ISU 205 = air to air, ISU 255 = Fossil Fuel, and ISU 335 = 40°F The fan in the air handler will continue to operate and blow cold air. That is because the thermostat assumes that the Aux Fossil Fuel heat is included in the duct system. With your system, the Fossil Fuel Aux is not included in the ducted system, therefor the fan needs to stop.
There needs to be an additional relay to stop the fan from operating when the compressor stops operating for heat below 40°F outdoor temperature. This is doable!
Thanks again Ed,
I think this is the exact problem that first happened when we tried to wire it up last year. Since it kept the fan on we were stumped and thought something was wrong, but not sure how to fix it.
It is no rush if this is a Monday thing, I'm swamped with the young kids on the weekend until they sleep so can't test too much anyways :).
I have added a RIB relay to be installed in the AirHandler for the attic. It is a double poll relay. DPDT
I have removed the T675A thermostat and used a different relay. one set of contacts do the Zone Valve as usual, the other set of contacts disconnect the G or Fan wire at the same time. Purchase this relay https://www.supplyhouse.com/Functional-Devices-RIB2401D-Enclosed-Pilot-Relay-10-Amp-DPDT-w-24-VAC-DC-120-VAC-Coil?_br_psugg_q=rib+relayand wire it this way
By breaking the Green wire from the thermostat to the air handler with the NC contacts on the RIB relay the fan will not operate when the boiler is heating the zone. You still make the heat relay do the same thing with the zone valve using the COM and NO contacts on the RIB.
I did not make that change on the bottom air handler, but you can do the same thing there too.
- 169 Indoor-Air Quality
- 50 Industry Classes