Carlin ez1 issues
                    Dadam
                    Member Posts: 1
            older Carlin ez1 burner
Runs for 3-5 seconds no flame, stops. Goes through restart process. No flame, good oil flow out the bleeder, no oil from outlet of pump. Any ideas, solenoid valve???. The run 3-5 seconds stop restart make me think controller perhaps
Plugged pump strainer , slipping dive coupling , my first thoughts …
solenoid valve, check coupling. Check for any leaks see if you’re sucking in air anywhere. Put a pump pressure gauge make sure you’re building pressure and holding it. Not much info to go off of
What's the voltage at the oil delay valve when powered?
What's powering the burner circuit, B1 from the aquastat, or TT at the Primary?
What model Primary?