Carlin ez1 issues
Dadam
Member Posts: 1
older Carlin ez1 burner
Runs for 3-5 seconds no flame, stops. Goes through restart process. No flame, good oil flow out the bleeder, no oil from outlet of pump. Any ideas, solenoid valve???. The run 3-5 seconds stop restart make me think controller perhaps
0
Comments
-
Plugged pump strainer , slipping dive coupling , my first thoughts …
There was an error rendering this rich post.
0 -
-
solenoid valve, check coupling. Check for any leaks see if you’re sucking in air anywhere. Put a pump pressure gauge make sure you’re building pressure and holding it. Not much info to go off of
0 -
What's the voltage at the oil delay valve when powered?
What's powering the burner circuit, B1 from the aquastat, or TT at the Primary?
What model Primary?