Steam Boiler Install 112,000 BTU

Rate my Install

ethicalpaul

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,363

    Can you post some pictures? Various angles. Stand back when taking pics.

    ethicalpaul
  • DaironHvacTech
    DaironHvacTech Member Posts: 4
    2967619317164804645_01.jpg
  • DaironHvacTech
    DaironHvacTech Member Posts: 4
    2994700629564572343~2.jpg
  • Steamhead
    Steamhead Member Posts: 17,758

    First mistake: You reduced the steam piping from 2-1/2" to 2". This can cause wet steam, banging, reduced efficiency etc. See pages 9-10 of the boiler manual, here:

    https://penncoboilers.com/sites/default/files/1305004%20PENNCO%2016%20IOM%20REV%20L.pdf

    There seems to be this lingering perception that steam boiler piping should all be 2". This is dead wrong. You have to follow the instructions. Also, the manufacturer may not honor the warranty if something goes wrong and the instructions were not followed.

    For more on this topic, get the following book:

    https://www.heatinghelp.com/store/detail/the-lost-art-of-steam-heating-revisited

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2DaironHvacTech
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,363

    Pressuretrol setting seems high. But hard to tell from picture

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,363

    Not a fan of coming out of the side of the header.

  • pedmec
    pedmec Member Posts: 1,199

    this is the perfect application for a drop header

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,078

    You worked hard and obviously take pride in your work. The boys are right on their comments. I give you a C +. If you repipe the header and near piping, I'll give you the opportunity to score as high as an A. If it works fine and runs OK, you can leave it but you are taking your chances on the warranty not being honored. Since, you DO seem to care, I'd repipe if I were you. Mad Dog

    DaironHvacTechCLambethicalpaul
  • DaironHvacTech
    DaironHvacTech Member Posts: 4

    Cool. Didn't know if I went a half inch smaller on pipe it will cause problems. I been using 2" and everything been working fine. I'll start using 2 1/2 after this boiler.

    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,078

    We all started somewhere.…

  • ethicalpaul
    ethicalpaul Member Posts: 7,621
    edited August 2024

    Well it's kind of complicated @Steamhead as you know.

    This is a 4 section Dunkirk design. It's the exact same as many other brands I believe, including Utica, which is probably the most commonly used brand for this design (at least around NJ).

    Utica calls for a single 2" supply and header for the 3 and 4 section. Yes, Pennco calls for 2-1/2" which will no doubt be generally better, but this boiler will work fine with 2" as long as the water quality is reasonable (as I proved with my old boiler even though it had a garbage "vertical" header).

    DaironHvacTech said:
    > Cool. Didn't know if I went a half inch smaller on pipe it will cause problems. I been using 2" and everything been working fine. I'll start using 2 1/2 after this boiler.

    @DaironHvacTech don't take the wrong lesson. The lesson is not to always use 2-1/2, the lesson is to read the instructions as Steamhead said. The instructions will tell you what to use for that size boiler from that manufacturer.

    Also, stop painting your pipes. And stop buying Dunkirk boilers for your customers. Get a Peerless or Weil-McClain (or a WM off-label such as Williamson). Those side-outlet Dunkirk types are more prone to surging (which is probably why Pennco says to use a 2-1/2" pipe, so they don't get angry calls—the problem is this causes unnecessary expense for you and your customers. You will get more jobs if you don't have to quote 2-1/2" pipe for a 112kbtu input boiler.

    Final questions @DaironHvacTech : How did you size that boiler? What was your skimming procedure? Once I know that I will give you a grade.

    image.png

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    bburdSTEAM DOCTORLRCCBJ
  • Steamhead
    Steamhead Member Posts: 17,758

    @ethicalpaul , in my experience the Utica/Columbia boilers shown in your diagram don't surge anywhere near as much when only using one 2" tapping. Maybe because they are a bit taller. Dunkirk/Pennco's instructions say to use 2-1/2" for steam risers and header, so we do. And we don't have issues.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaulMad Dog_2
  • ethicalpaul
    ethicalpaul Member Posts: 7,621
    edited August 2024

    "we don't have issues" is confirmation bias as you and your partner well know 😃 You wouldn't have issues with 3" pipes either.

    But I'm not sure what you are saying. Are you saying the Pennco is using different castings than Utica? Are you saying all of these boilers do better with a single tapping than with two tappings? Are you saying Utica is playing a bit fast and loose? (I can believe it) Thanks in advance for clarifying what you're saying, I greatly respect your opinion and experience.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Steamhead
    Steamhead Member Posts: 17,758

    The castings are different. I've known that for a long time. Just because they both use side outlets doesn't mean they have the same castings.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaulMad Dog_2
  • ethicalpaul
    ethicalpaul Member Posts: 7,621

    Thank you sir, I was under the mistaken impression that all these Dunkirk style boilers were using the same Dunkirk castings.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,078

    What about Hart & Crouse? Mad Dog