boiler uses oil burner that is equipped with return nozzle
Khaled
Khaled Member Posts: 4
Picture for the nozzle attached to a box with moving pressure regulation parts
this regulator is stuck, even with max inlet pressure; no oil is flowing out of the return pipe
what is the name of this box and how to order it?
  • retiredguy
    retiredguy Member Posts: 1,086
    edited August 2024
    If you do not know how to work on this nozzle assembly, maybe you should call someone who is familiar with this arrangement. A bypass nozzle equipped burner can have a large oil input and mistakes usually happen quickly, say in 'the blink of an eye". I would not want that mistake to happen when I was doing the repair. An oil burner is not a thing to play or experiment with. I could tell you how to clean the nozzle to see if it is plugged but if you have the necessary experience you should already know how to clean it. BTW what is the name and model of the burner?
    Steamhead Member Posts: 18,393
    This!
    @Khaled , where are you located? We might know someone who can help.
    Consulting
    EBEBRATT-Ed Member Posts: 20,070
    That may be a Riello burner
  • Khaled
    edited August 2024
    thank you all for the reply.. appreciate your concern.. this is just a burner, easy to handle without any risk, I need to replace the nozzles and the regulators.
    Steamhead .. (no comment) !! the burners are used in a factory in LIBYA
    just seeking advice from your experts
    Ebebratt-ed Ya.. it is Riello RL130/M with control on the return pressure
    any idea about this regulator part/order no. ?
    @Khaled
    I am not sure it has been a long time since I worked on a Reillo Oil burner that size. If I recall correctly the nozzle adapter had 2 threaded caps on it with springs inside. The burner I was working on had a bad after drip. I called Reillo and they told me to take the threaded caps off and remove the springs and re install the caps. I wanted to talk to Ross Crompton but he had retired but the fellow I talked to told me what to do and it fixed the problem. They could not even tell me what the springs did.
    I don't know if it helps your problem.
    I talked with Riello in Toronto Canada
  • ScottSecor
    ScottSecor Member Posts: 1,030
    Not sure I have ever worked on a commercial Riello oil burner. However, we have worked on numerous oil burners with these BPS nozzles. Might not be what you have, but I suspect they work the same way. Might be a helpful reference.
    https://www.monarchnozzles.com/index.php/en/portfolio/portfolio-listing/item/45-bps
  • Khaled
    Thank you for the info.
    @ EBEBRATT-ED
    I tried this solution before I write this question. and even removed the internal seized stem,, it did solve the issue partially but still there is misfiring during startups.. Replacements is really essential. The other thing is that the assembly contains rubber seals, lost the elasticity over time, not forgetting the operating temperature in that area of the burner.
    @ ScottSecor
    Ya that is the nozzle with return .. and the assembly contains another return mechanism
    different suppliers.. reply .. do not supply them anymore
    HVACNUT Member Posts: 7,401
    Have you contacted Riello? There must be a download for the manual, with replacement parts listed.
  • Khaled
    Updates .. manufacturer sent new nozzles and new nozzle holders, simple holders dose not contain return mechanism..
    with some fuel/air adjustment.. the three boilers are properly working.
    I appreciate your efforts in sharing your knowledge and helping me out. It’s great to be part of such a supportive community!
    Thanks again for your time and support!
    Best regards,
    Glad it is fixed. Sounds like they made some changes.