Why is this spewing water ?
sldamiano
sldamiano Member Posts: 37
edited July 2024 in Strictly Steam
water is coming out of the boiler from that corroded piece. I’m not familiar with this system.
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,416
    Not enough information provided. Is there an indirect water heater connected to this boiler? Or a tankless coil? Take a bunch of pictures of different things around there, from further back and from different angles. Regardless, you'll need to get a pro in there.
  • sldamiano
    IMG_3771.jpeg IMG_3773.jpeg IMG_3774.jpeg IMG_3776.jpeg IMG_3775.jpeg IMG_3772.jpeg
    They get here tomorrow. Just trying to get the water flow to stop for now and curious why it’s coming out of that valve
  • pedmec
    pedmec Member Posts: 1,238
    Because it's most likely defective and looks like it's been leaking for a long time. But you could also have a chicken or the egg scenario where its discharging because it's doing its job. Either way i think you need to replace it first and then you can continue on to find if there is another problem that is causing it to drip. And add the discharge drain tube. you don't want that to unload wide open and burn the **** out of you.
    Jamie Hall Member Posts: 26,330
    And in case you haven't gathered, that's the safety pressure and temperature relief valve for the whole system. You do NOT want that releasing.
    Steamhead Member Posts: 17,947
    First thing I'd check is the pressure in that Extrol tank. If that's low it can cause the safety valve to "weep".
    Consulting
    HomerJSmith
  • STEAM DOCTOR
    Would have to assume that the valve itself is defective. The boiler is presumably off. Expansion tank is only a player, when the boiler is on. You can shut the water intake.
  • Lance
    Lance Member Posts: 324
    Any leak on a sealed hydronic system is subject to a pressure problem or a material or labor defect. test with accurate working gauges. Don't trust what is there. The question of a control leak can be; is it the cause, or its doing its job for safety? never assume it can't be operator or installer error. Also, for those baffling situations, look for that intermittent cause that may not always be present. Remember a valve may seem open or closed but is not. A pump may work, but not enough, a change may have occurred that was not recognized as a cause.
    imagine a gas control that overfires twice its rate, but only now and then. I have found check valves stuck, worse, installed backwards. Regulators that failed, expansion tanks that test good but don't actually see the water pressure, or the diaphragm is stuck closed.
  • Grallert
    Grallert Member Posts: 983
    my money is on the expansion tank
    HomerJSmith
  • Karl Reynolds
    Karl Reynolds Member Posts: 76
    Agree with Grallert. The date code on the expansion tank is the 341st day of 1987. Should change the T&P at the same time.
    HomerJSmith
