Drop header
Hey all, we are installing two new steam boilers along with a drop header. The header consists of a 6 inch pipe caped at both ends. I will have both boilers connected at 6 inches away from the end, one at both ends and 2 steam outlets to the building 18 inches away from those. Also, I will have a drip leg c/w steam trap directly underneath boiler header connections. Does anyone see any issues with what I am planning to do.
Comments
-
0
-
That won't work right. Any water that the drip legs don't catch will travel toward the system take-offs.
The right way is just like we'd pipe a boiler. Start at one end of the header with your two boiler lines. Then connect the two steam mains, and end with a single drip leg. I'd make the drip leg 2". Pitch the whole header down from the first boiler connection to the drip leg.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting3 -
-
That's correct.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks for the advice.
0 -
sim, how is the condensate water returning to the boilers?
0 -
Thru a condensate tank which is vented to outside.
0 -
-
I call those the Mad Dog Bazooka Header. With a 6" Trunk line, go with a 2 1/2" drip minimum. Send us final results. Mad Dog 🐕
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements