Is this an issue?
pjyorks
pjyorks Member Posts: 8
edited July 2024 in Strictly Steam
In watching and reading Dan Holohan, it seems our boiler is not piped correctly. Even looking at the 90 degree fitting on the right it looks like it failed at one point.
Would you re-pipe this boiler?
    Steamhead Member Posts: 18,391
    Yes! Not only is the order of riser connections to the header wrong, but the header is 2" and I believe it should be 3". Check the manual.
    One would think basic literacy would be required in our business, but apparently some don't agree……..
    Consulting
    delcrossvpjyorks
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,582
    Not liking the flue piping either.
  • bburd
    bburd Member Posts: 1,293
    @pjyorks If properly piped, that system should heat quickly, evenly and quietly. Piped as it is, I would expect gurgling, hammering, slow and uneven heating and water spitting from air vents. How does it perform?
    Bburd
    HVACNUT Member Posts: 7,382
    edited July 2024
    And I don't think the Hartford Loop should be sleeping… if that's supposed to be a Hartford Loop.