I am looking for the right breaker lock in clip for the right breaker in this interior. I want to use this panelboard as a transfer switch so both breakers will be back fed so both will require lock in clips. I'm not sure if this extra structure is only the rejection feature that allows tandem breakers to only fit in these slot or if there is some other accessory that could attach here too but I think what I need is a lock in clip that is compatible with a tandem breaker slot. Anyone know Square D parts well enough to point me to the right part? The clip holding in the left breaker will not work here because of the extra structure next to the rail.







Schneider doesn't seem to be answering my question about what is the right clip for this application. I'm curious if there are other accessories that attach to that structure besides a tandem breaker.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329
    I don't know exactly what you need but see the attached. Look in "accessories" Pg 73 ish I think what you need may be there.
    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399
    It doesn't look like any of those clips will work. The PK2MB white plastic block won't work because of the structure for the hook on tandem breakers and the metal brackets don't appear to line up with the interior screws, they look like they are for interiors with 2 rows of breakers (I don't know what type S1 and S2 mean). I hope I'm wrong but I looked over what I could find in the catalog a lot before asking.
  • 109A_5
    109A_5 Posts: 4,759
    Hello @mattmia2,
    From your picture, I'm thinking the panel you have is not intended to have the 2nd breaker added to the left side of the existing one with the mutually exclusive mechanical interlock attachment. Or the existing breaker with the mutually exclusive mechanical interlock attachment needs to be moved to the right hand slot so the interlock works properly with a 2nd breaker to its left for transfer switch type service.




    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Posts: 4,759
    Hello @mattmia2,

    If the bus bars are there, it looks to me like the additional breaker goes to the left of the existing breaker, with the same white retainer block (PK2MD) and a screw.





    Page 74 of the @EBEBRATT-Ed provided catalog PDF. document.




    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Posts: 18,399
    109A_5 said:

    Hello @mattmia2,

    If the bus bars are there, it looks to me like the additional breaker goes to the left of the existing breaker, with the same white retainer block (PK2MD) and a screw.





    Page 74 of the @EBEBRATT-Ed provided catalog PDF. document.




    it is a 2 space 4 ckt panel, though the interior has 8 spaces, the bus is only 4.
  • mattmia2
    mattmia2 Posts: 18,399
    I finally heard back from Schneider. They say that there is no lock in clip for the right breaker in that panel.
  • ChrisJ
    ChrisJ Posts: 17,763
    mattmia2 said:

    I finally heard back from Schneider. They say that there is no lock in clip for the right breaker in that panel.

    Do they make an actual interlock kit specifically for that panel?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Posts: 18,399
    ChrisJ said:


    mattmia2 said:

    I finally heard back from Schneider. They say that there is no lock in clip for the right breaker in that panel.

    Do they make an actual interlock kit specifically for that panel?
    I don't think so but I have yet to find a decoder of what accessories work with what panel. The interlock kit for that style of panel just has 2 of the white plastic blocks that screw to the side of the interior and the interlock bracket that clips on to the breaker for about twice what it costs to buy the separate parts.
  • pecmsg
    pecmsg Posts: 7,634
    If that panel was not designed as a Transfer switch then do not use it as such. 
    Purchase an appropriate Transfer Switch and have it installed by a licensed electrician. 
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329
    @mattmia2

    Back feed breakers are supposed to be held in by a clip or screw because if they become disconnected from the panel the breaker will be live (I am sure you know this), even though the breaker will be held in place by the panel cover.

    There is a company on the internet that MFGs interlocks for older panels that the MFG does not have them available. If I find it I will post.
    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    @mattmia2

    Back feed breakers are supposed to be held in by a clip or screw because if they become disconnected from the panel the breaker will be live (I am sure you know this), even though the breaker will be held in place by the panel cover.

    There is a company on the internet that MFGs interlocks for older panels that the MFG does not have them available. If I find it I will post.

    Since it is the breaker that will be fed from the portable generator from an inlet about a foot away I am more concerned with technical compliance with the code than safety. If you haven't shut down or disconnected the generator and are digging in this panelboard there are probably bigger safety issues with what you are doing.
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329
    @mattmia2 Google this company "Interlock Kit"

    Maybe they can help you out. They make generator interlock kits.


    I had a Bryant "BR" sub panel I installed on a job and bought it with a 100 amp main breaker that was installed as a "back feed breaker" with a screw to hold the breaker in place. And I bough the interlock kit to mount on the panel cover.

    I also bought a "back feed breaker kit" (it's just another screw) and bought a two pole 30 amp breaker to install as the generator input.

    The 100 amp breaker had a hole in it to accept the screw. Unfortunately the 30 amp has no such hole in the breaker even though both breakers are just standard 2 pole breakers and are exactly the same physical size. I think I later found that 60s and up have the hole and 50s and under don't.

    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    This is what I ended up doing:

    image.png

    I could have used @EBEBRATT-Ed 's greenlee punches when I was chasing between the boxes because the ko in that position of the old pannelboard was only 1.25" and I needed a 1.5" nipple for the fill.

    image.png

    I still need to fix the directories, the tape is the old circuit number

    image.png image.png image.png

    I did have @EBEBRATT-Ed 's punches to make this hole, i have a grommet with a hole on the cord and i can swap the solid for the grommet with the hole to plug the generator in.

    image.png

    I don't know why my phone decided it wanted to go in potato focus mode here.

  • ChrisJ
    ChrisJ Posts: 17,763

    What's the reason for the large enclosure to house a standard metal box for your generator receptacle?

    I used a small downfacing outdoor receptacle made for it that has a little spring loaded flap that covers it when not in use. It's a 50A 3 prong + ground.

    471591876_10162087607681253_6780521683145783768_n.jpg

    51ZVscRKsJL._AC_SL1010_.jpg

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    PeteA
  • mattmia2
    mattmia2 Posts: 18,399
    edited August 2025

    I wanted something that was actually waterproof, not sort of waterproof if it isn't raining too hard or too windy and i put the right accessories on the cord end plug. I seem to recall those were insanely expensive and only off brands too.

  • ChrisJ
    ChrisJ Posts: 17,763

    It doesn't need to be water proof. It's not going under water.

    It just needs to shed water like a roof. Even fairly hard wind driven rain isn't going to climb vertically up that plug.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    PeteA
  • mattmia2
    mattmia2 Posts: 18,399

    well i said i hadn't used this yet on monday. today the power is out.

    i very much knew what i was doing and managed to screw it up. i connected the subpanel conductors to the commercial mains breaker and the feed from the commercial mains to the xfer switch bus. i had to do a quick rewire by flashlight.

    bjohnhy
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I helped a former co-worker hook up a generator about 6 years ago. It runs to test every week. His wife had to have it.

    Talked with him a month ago and they have never needed it.

  • mattmia2
    mattmia2 Posts: 18,399
    edited September 4

    here the utility is so far behind on maintaining their stuff that when there is a moderate thunderstorm it goes out for a couple days because they have like a couple hundred major outages so it takes them days to work through all of them.

    the time lapse radar and the outage map are the same map.

    it hadn't gone out since i think sometime in 2042 but it would go out for several days once or twice a year and i was getting tired of setting up cords every time. I would have used an automatic switch that was flipped by the generator but those kind of were still backordered for months when i stared this project.

    kinda wishing i finished my project to build another generator with that ~24hp kohler i bought 6 months or so ago so i could start the ac with it now.

  • mattmia2
    mattmia2 Posts: 18,399

    oh, and dte only did trimming and replacement of some of the worst of the decaying parts here in ann arbor because we started organizing to form a public power utility