Current radiant setup
Flyingpoet
Member Posts: 4
Hi,
I’m having issues with my current radiant system after years of it seemingly working properly. I tried replacing the pump but same problem of no heat. The gauges show water flow through all the zones but it’s just pumping cold water and the gauge on the outlet of the mixing valve shows cold. The gauge on the hot supply to the mixing valve is hit but then it’s cold coming out of the mixing valve. Before I replace the mixing valve I wanted to run this setup by everyone. To me it seems like the system is piped incorrectly with the pump seemingly bypassing the mixing valve pulling return water straight into the supply before hitting the mixing valve but it had worked for many years so maybe I’m wrong…?
Any thoughts or help on if I need to have this setup all redone or if it is correct and may just be a faulty mixing valve.
Do you have a pressure gauge? What does it show?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Boiler pressure gauge is 25psi but there are no other pressure gauges. The only gauges on the radiant are the supply, mixer, and return temperatures and the GPM flow rates on each zone. Supply temp reading 120F, mixer temp reading 62F, return reading 60F and flow rates are .5GPM to .75GPM depending on zone. If I unplug the circulating pump the flow rates go to 0.0
Mixing valves do stick from time to time. The flow meters indicate flow moving through the loops. What temperature is the boiler running?
You may have enough valves around it to isolate and disassemble without a complete draindown. Does the red knob turn easily?Bob "hot rod" Rohr
The boiler is running 160F-180F. Yes the red knob turns easily. It’s turned now to the highest set point temp but still isn’t raising the temperature of the water flowing in the radiant system. I can replace the mixing valve but also just wanted to confirm that the setup with the pump being parallel to the mixing valve is acceptable?
I mean it did work before but it just seems to me like the pump should be in line/after the mixer valve and I can’t figure out how the current configuration would work properly…I was hoping to get confirmation from the forum that this setup makes sense.
The pump orientation is a little odd, I'll agree -- but it should work if the mixing valve is working properly. And it would be my guess that it isn't. Do you have, or have access to, a good IR thermometer? If so, compare the temperature at the two inlets to the mixing valve and the outlet.Br. Jamie, osb
That pump is doing nothing to draw water through the mixing valve. The pump bypasses the mixing valve. The pump should be located on the mixed outlet of the mixing valve.
You say it worked before, but something's not right here.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Alan, that’s exactly what I think….i really don’t understand how it worked properly for the last few years or why it was installed that way.0
That looks like a factory built mixing module , possibly from Watts since it connects directly to their manifold spacing?
If it has worked properly for years??
Id remove the pump, check impeller, and rebuild the mix valve. Two fairly easy tasksBob "hot rod" Rohr
There are some blue handled ball valves hiding behind the first vertical pipe on the right. Are they open or closed ?
And why is that Legend valve in the foreground closed?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
- 121 Chimneys & Flues
- 15.8K Strictly Steam