Bosch IDS Heat Pump + hydronic backup heat Aquecoil
marios
marios Member Posts: 1
I recently had a Bosch IDS 2.0 5-ton heat pump and air handler (BOVA-60HDN1-M20G) installed as part of my ducted HVAC system. Along with this, an Aquecoil hydronic coil was added for backup heating purposes. This way we have heat in case of a power loss (a somewhat common occurrence in my area of Connecticut) or if temperatures drop below 15F. We utilize an IBC propane boiler for our hot water needs and have incorporated an additional loop/pump specifically for the HVAC Aquecoil system.
However, the installer is struggling integrating this setup with a Honeywell T10+ thermostat. What's the proper thermostat wiring for this configuration? Specifically, should the hydronic coil be configured as AUX heat, similar to an electric strip heater, or does this setup require a dual-fuel system approach? I'm also looking for any wiring diagrams or guidance that could assist in this matter.
Ideally, I'd like to setup a system that automatically switches to backup heat when outdoor temperatures drop 20F or below. Given that propane is here quite a bit more costly than electricity—approximately 2 to 3 times more expensive per BTU—I aim to operate the system as economically as feasible. Any insights or advice on how to achieve this, without overly complicating the setup, would be greatly appreciated.
Thanks
  • yellowdog
    yellowdog Member Posts: 293
    Bosch will provide you with all of the wiring diagrams that you need. Why are people afraid to call the manufacturer for help? The system was probably bought from FW Webb. Who is the installers salesman? They should also provide wiring diagrams.
    tim smith
  • Ironman
    Ironman Member Posts: 7,903
    edited February 2024
    The T10 should bring on the hydronic when set to “Emergency Heat” by energizing a relay that signals the boiler and pump to come on.
    Do you have a generator that’s capable of powering the system during a power outage? You’ll still need power to run the hydronic system and the AHU during a power failure.
    This is the best solution:
    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Taco%20-%20HAFC201-4%20-%20Product%20Overview.pdf
    Bob Boan
  • leekshuster
    leekshuster Member Posts: 2
    While I realize what I'm about to share is a forced-air-based HVAC solution, it DOES share some common elements with the Bosch IDS system @marios mentions.
    In the fall of 2023, my daughter installed the same Bosch IDS 2.0 Heat pump (outdoor unit -- inverter/compressor) to replace her 22-year-old AC-only DX unit. At the same time, we decided to replace the (Indoor) Tempstar forced-air (ducted) furnace which was powered by natural gas.
    Indoors, a new forced-air furnace (Amana) has an "A-frame" coil that connects to the Bosch which can cover all central (space) Cooling or Heating. In our area (Utah) the local utility provides rebate incentives to encourage "Dual-Fuel" or hybrid solutions. (Check your local area.) Bosch overs a complete turn-key solution, but an Amana/Goodman (indoor) solution was chosen to save her some $$$.
    <<DHW is by a separate (stand-alone) direct-fired 53-gal Rheem.>>
    There is an optional resistance-heat "strip" backup option which we did not employ, as natural gas is our "AUX" backup fuel of choice. The "balance point" or cutover from electric (air-to-air heat pump) energy to "AUX" is currently set at 25 .F. At that point it is cheaper to burn nat gas (AUX), as the heat pump COP starts to decrease. (But the Bosch IDS can continue running down to our Design Temp of 10 .F (and below) but at reduced COP.)
    I was surprised to find how easy the system was to control. In our case, the contractor recommended an Ecobee Smart thermostat. (Which also had local utility rebates). It turns out there is quite a bit of hidden "intelligence" built into the Bosch IDS to control the variable speed inverter-compressor and allows for just about any thermostat to be specified. The Ecobee easily allows the homeowner to specify the AUX balance point. So far this heating season, the comfort levels are improved. The Ecobee-controlled transfer between "PRIMARY" and "AUX" is seemless and is undetectable unless you observe the IDS fan outside.
    An added benefit, the Bosch IDS heat pump is taking advantage of excess net-metered, roof-top solar PV power. It is too early to accurately report, but this winter's natural gas CH heating is way down, while electricity is up. Next summer's cooling (AC) season should show reduced electricity when solar PV peaks.
    The trend is for vendors to specify total turn-key solutions, but that makes "open" custom solutions harder to design, control and install. In my daughter's case, we were able to save $$$ by not going "all Bosch," including their thermostat.
    I'm not trying to specifically recommend brands or products here on the Wall. Understand, I am sorry I can not offer specific wiring advice to marios or the contractor, with a slightly different system. I'm just trying to share our positive experiences for others to draw from. I'm certain once homeowners, contractors, and suppliers get more experience with heat pumps -- We will share our experiences, and more affordable, reliable solutions will become available.
  • BradHotNCold
    BradHotNCold Member Posts: 82
    This appears to be close to our needs in central CT! Good post!
  • DCContrarian
    DCContrarian Member Posts: 1,457
    Just googling, it seems like average electricity price in Connecticut is $0.37/kWh and average propane price is about $4.10. A gallon of propane is 91,500 BTUs, propane furnaces tend to have about 90% efficiency, so that's about $50 per million BTUs delivered. A kWh of electricity equals 3412 BTU of heat, so that's roughly $108 per million BTUs. So the heat pump is cheaper when the COP is 2.16 or greater.
    Performance data for that heat pump is here: https://ashp.neep.org/#!/product/66113/7/25000/95/7500/0///0
    The COP is 2.16 at 17F, so 17F would be your switchover point.
    There are two things that happen with heat pumps when the temperature drops. Their efficiency drops, and their output drops. If the efficiency drops below the break-even point — in this case COP 2.16 — what you want to do is turn off the heat pump and use your backup heat. If the output drops below the heating load, but the efficiency still favors the heat pump, you want to get as much heat as you can out of the heat pump and only supplement it with the backup heat.
    The control strategy for the two situations is different.
    In the first situation you need an outdoor sensor to turn off the heat pump at the break-even temperature.
    In the second, you can sense that the heat pump isn't meeting the heating load because it won't be able to meet the heating setpoint. That's the classic backup heat scenario, you have a thermostat with two setpoints a degree or two apart and the backup heat comes on at the lower setpoint.
  • GW
    GW Member Posts: 5,184
    some dudes really struggle with low voltage controls and wiring. We generally use the basic RIB relay, to call on the boiler. As stated, the AUX will kick the boiler on. You can also keep the compressor going or drop it out based on the thermostat settings.
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com