If our community has helped you, please consider making a contribution to support this website.  Thanks!
CONTROL MODULE IGNITION 120V FOR CGA SERIES 1107-2 | WEIL MCLAIN
                    rvolcom75
                    Member Posts: 8
                    My boiler isn’t responding at all. I followed the ladder diagram in the troubleshooting section of the manual to where it had check for 120v at the circulator plug on the controller which I did not get a reading from. I’m just not super familiar and was wondering if there is anything else that would cause it to not respond. There is one green status light that stays on at all times.
            post a picture of that green LED and its controller,
sounds like no call for heat,
batteries fresh in the thermostat?
picture of the stat alsoknown to beat dead horses0 -
            Hello @rvolcom75,
As @neilc said, "sounds like no call for heat". If the system has one, Zone valve controller issue ?
https://www.weil-mclain.com/sites/default/files/field-file/CGa Series 3 Boiler Manual 0520.pdf
One Pipe System0 -
            Shoot alright give me one sec I’ll post pictures.0
            The green power light stays on, never flashes0
            Hello @rvolcom75,
I see two transformers, one under the boiler control board, probably is OK (control board has power). Assuming none of the zones work I would verify there is 24 VAC from the other transformer.
If you jumper the End Switch does the boiler fire up ?
One Pipe System0 -
            Hello @rvolcom75,
Typical circuit. Yours appears to not have zone 4 and 5 and the associated extra parts.
One Pipe System0 -
            Just to be clear. I can make contact with a jumper between the two legs that you demonstrated above while the boiler is live still or should I shut it off at the panel and install a jumper and then restore power0
            Hello @rvolcom75,
Either way, the 24 VAC should not hurt you. You can make the connection with an insulated wire or tool. But if you want to be on the safe side shut it all off and add the jumper then re-energize and see if the boiler starts up.
Is there 24 VAC at the transformer terminals pictured ?
One Pipe System0 -
            Sorry for the late response working some long days. I’m about to run out and check now0
            Ok I tried the jumper wire doesn’t appear to of made a difference0
One Pipe System0
 - 87.2K THE MAIN WALL
 - 118 Chimneys & Flues
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 73 Pipe Deterioration
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
