Gas boiler. It's a HB smith
Hi everyone i have a Gas boiler that comes on burns for 20 minutes
Then goes out and don't come back on
I changed the board and the thermocouple
It came on for a awhile and shut down and will mot come change out the board twice
when you say does not comeback on what do you specifically mean? what kind of boiler are we talking about here?0
Is there a control that is locking out for some safety or other reason that needs to be reset? There are many gas boiler controls that will "RESET" by cycling off the power to the control. Does this sound like your problem? When did the problem start? Does turning the power off and back on get the burner to light? What is the model number of the boiler or perhaps the burner control?
Does your gas valve use a standing pilot? (constant pilot flame burning ignition)
Is there an ignition control that lights the pilot each time the burner lights?Edward Young Retired
I have a HB smith boiler model number G100-w-6 con it use to work if I cut the power off and back on then it completely stopped that's when I replaced the thermocouple and the board it work for 20 minutes the it went out I still had a flame on the pilot but no burners found out the board was no good again now the same thing has happened
Yes a standing pilot0
This is the boiler0
What "board" did you replace?All Steamed Up, Inc.
Consulting0 -
By "board" do you mean the ignition control?0
If the gray box is "the board" then you must have something wired incorrectly. Those Honeywell Aquastats should last for over 20 years in most heaters. even longer...
Can you tale a picture of what you re calling "the board" with the cover off so we can see the wires inside?
The control board
This has no control board, it has a bunch of safeties and operating controls wired together point to point.0
1. You should get someone to clean this and test the safeties, though a gas boiler arguably doesn't need annual service like an oil burner, it still needs to be cleaned and tested from time to time and this is over due.
2. What thermostat is controlling this? Does it stay on if you jumper the thermostat connection, usually T-T?0 -
That's the "roll-out" safety. If this thing is going bad, there is something else VERY wrong. You need to shut it down and call a pro NOW. Where are you located- we might know someone........All Steamed Up, Inc.
Consulting2