Gas valve isn't working
Rich Davis_2
Member Posts: 128
in Gas Heating
Woke up this morning 25 deg outside and the boiler wasn't working. I have a Trangle Tube PS60 it was showing a E 03 I couldn't feel or hear the gas valve clicking, checked the troubleshooters guide and said gas valve cable not properly connected. So I checked the cable and seems OK at both ends. Checked both fuses they seem OK too. So how I determine if it's the cable or the valve. How much voltage should I get on the connections of the cable and should I be able to check the valve with is disconnected? Any suggestions would be greatly appreciated
I checked the resistance on the valve and the readings are with an ohm of that the manual says. I guess my question is how much voltage should I be getting going to the valve?0
24 VAC is the standard votage for standard valves. inless you have some variable input that operates on DC voltage with the venter motor.Rich Davis_2 said:I checked the resistance on the valve and the readings are with an ohm of that the manual says. I guess my question is how much voltage should I be getting going to the valve?
The Trouble sooting Guide for the PS60 that I found indicates that a sensor is open or shorted for a E_31. It does not have a E031 code.
Sorry about the confusion it was a E-03.0