Gas valve isn't working
Rich Davis_2
Member Posts: 121
in Gas Heating
Woke up this morning 25 deg outside and the boiler wasn't working. I have a Trangle Tube PS60 it was showing a E 03 I couldn't feel or hear the gas valve clicking, checked the troubleshooters guide and said gas valve cable not properly connected. So I checked the cable and seems OK at both ends. Checked both fuses they seem OK too. So how I determine if it's the cable or the valve. How much voltage should I get on the connections of the cable and should I be able to check the valve with is disconnected? Any suggestions would be greatly appreciated
0
Comments
-
I checked the resistance on the valve and the readings are with an ohm of that the manual says. I guess my question is how much voltage should I be getting going to the valve?0
-
0
-
24 VAC is the standard votage for standard valves. inless you have some variable input that operates on DC voltage with the venter motor.Rich Davis_2 said:I checked the resistance on the valve and the readings are with an ohm of that the manual says. I guess my question is how much voltage should I be getting going to the valve?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
The Trouble sooting Guide for the PS60 that I found indicates that a sensor is open or shorted for a E_31. It does not have a E031 code.



Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Sorry about the confusion it was a E-03.0
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 117 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.7K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements