Any reason I can't put a Gorton 2 at the TOP of a riser instead of the bottom?

Jells
Jells Member Posts: 576
I want to increase the venting of the riser furthest from the boiler, but the main vent is inside the wall of the basement tenant's apartment and access is a PITA both physically and dealing with them. There's 2 risers from that point feeding 5 bedrooms upstairs, on one of the rads on the top floor I have previously added a tee between valve and union for a smaller extra vent. Now I'm thinking: why not put the Gorton 2 there? Any reason? Is it noisy?

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,658
    This is America 🇺🇸 Jells...you can do anything you want.  I won't call the Steam Vent police on ya.ha ha 🤣 😆 😅 Mad Dog 🐕 
  • dko
    dko Member Posts: 668
    someone texted me similar thing too

    "can I put a gorton 2 instead?"

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,658
    That works...Do the same the thing when the old vent is buried or covered in asbestos.  Mad Dog 🐕 
  • Jamie Hall
    Jamie Hall Member Posts: 25,365
    Actually, will work as well -- or better!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Jells
    Jells Member Posts: 576
    Jamie Hall said:
    Actually, will work as well -- or better!
    So why isn't it SOP?  On the 2-in riser without radiators that heats the bathrooms in the same house, there's just a vent at the top of the pipe in the top bathroom like a foot from the ceiling. Why isn't that done on every riser?

    For what it's worth, on most of the top floor radiators in the house I've already tapped the side near the valve and added another MOM radiator valve there with no port screwed in.

    This house is a mess. I'll probably post more of my thermometer reading graphs for people to read like tea leaves.
  • Jamie Hall
    Jamie Hall Member Posts: 25,365
    Why not SOP? Good question.... except that maybe folks don't like to see big main vents in the quality side of the house...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ChrisJ
    ChrisJ Member Posts: 16,375

    Why not SOP? Good question.... except that maybe folks don't like to see big main vents in the quality side of the house...

    Speak for your self!!!!

    ;)

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    delcrossvTezakCanucker
  • Jamie Hall
    Jamie Hall Member Posts: 25,365
    Look. When I was a kid, lo these many years ago, we never went into the kitchen, never mind the basement -- and the yard man and the cook who was also the maid never came into the rest of the house, except to do housework.

    Except of course, being kids, we did...

    That was a different universe, or at least a different planet...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ChrisJ
    ChrisJ Member Posts: 16,375
    edited January 2024
    Look. When I was a kid, lo these many years ago, we never went into the kitchen, never mind the basement -- and the yard man and the cook who was also the maid never came into the rest of the house, except to do housework. Except of course, being kids, we did... That was a different universe, or at least a different planet...

    Not sure about a different universe as much as a different tax bracket.


    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    bburddelcrossv
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,974
    Never see a rad piped like the picture above. Basically a 1 pipe system. Both the supply and return are piped to the same riser.
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,375
    Never see a rad piped like the picture above. Basically a 1 pipe system. Both the supply and return are piped to the same riser.
    I had actually thought about trying that.
    The reasoning was because I thought I could control the supply of steam but the condensate isn't interrupted.


    It looks like I wasn't the first one to have the idea and I guess it works.


    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,477
    edited January 2024
    On long runouts with a hard to heat radiator, we've swapped the radiator valve for a tee with a main vent on top and a straight valve to the radiator on the bull.
    Jells
  • Jells
    Jells Member Posts: 576

    Never see a rad piped like the picture above. Basically a 1 pipe system. Both the supply and return are piped to the same riser.

    So what's that device in the lower line on lower right, a check valve to release the condensate?
  • ChrisJ
    ChrisJ Member Posts: 16,375
    Jells said:
    Never see a rad piped like the picture above. Basically a 1 pipe system. Both the supply and return are piped to the same riser.
    So what's that device in the lower line on lower right, a check valve to release the condensate?
    Looks like a steam trap.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Jells
    Jells Member Posts: 576
    ChrisJ said:


    Jells said:

    Never see a rad piped like the picture above. Basically a 1 pipe system. Both the supply and return are piped to the same riser.

    So what's that device in the lower line on lower right, a check valve to release the condensate?

    Looks like a steam trap.

    No idea what that is, and I'm OK with that. Simple one pipe is more than I can deal with!
  • Jamie Hall
    Jamie Hall Member Posts: 25,365
    ChrisJ said:



    Look. When I was a kid, lo these many years ago, we never went into the kitchen, never mind the basement -- and the yard man and the cook who was also the maid never came into the rest of the house, except to do housework.

    Except of course, being kids, we did...

    That was a different universe, or at least a different planet...

    Not sure about a different universe as much as a different tax bracket.




    Much more a different planet. Family had had money, but the Great Depression did that in. We were lucky to keep the farm at all, and the cook and yard man lived there as well. We all just did what we could. On top of that, there was a war on, and no men around except me (much too young to be much help) and the yard man (too old, German name). We managed.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    bburdGrallertLong Beach Ed
  • Jells
    Jells Member Posts: 576
    edited January 2024

    ChrisJ said:



    Look. When I was a kid, lo these many years ago, we never went into the kitchen, never mind the basement -- and the yard man and the cook who was also the maid never came into the rest of the house, except to do housework.

    Except of course, being kids, we did...

    That was a different universe, or at least a different planet...

    Not sure about a different universe as much as a different tax bracket.




    Much more a different planet. Family had had money, but the Great Depression did that in. We were lucky to keep the farm at all, and the cook and yard man lived there as well. We all just did what we could. On top of that, there was a war on, and no men around except me (much too young to be much help) and the yard man (too old, German name). We managed.
    Yeah, full time household help was a normal middle class thing up until maybe the 60s. Think about all the TV families that had a full time housekeeper! I hear from South Asians that even today you have to be pretty low on the scale to NOT have servants! Same in many parts of south and central America.
  • Gordo
    Gordo Member Posts: 857
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • Sylvain
    Sylvain Member Posts: 154
    I guess it is a SOP to vent the risers in high buildings.