Commercial water heating, storage tank vs indirect
Hello, I do a lot of commercial service and installs. I frequently see DHW boilers (a LOT of burkay copper coil) to one or two storage tanks for buildings hot water. I rarely see an indirect or direct fire water heaters. I am curious what the advantages are to the storage tank system vs. an indirect or direct fire tank type. I’ve done lots of googling and can’t find anything.
Thanks!
    hot_rod Member Posts: 27,292
    indirect tanks  with a coil inside more expensive to manufacture
    bburdNgriswold
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,065
    Hi, As a very general rule, anything that has storage will give less temperature fluctuation than any sort of on demand approach... assuming the storage is correctly sized for the load. This matters for showers, where people will feel a one degree change, less so for other uses. Not sure that's what you were asking about though :)
    Yours, Larry
    Ngriswold
  • Teemok
    Teemok Member, Email Confirmation Posts: 757
    In addition to $$$. Volume water heaters will recover the tank faster. Generally the temperature difference between flame to domestic water is larger than the flame to return hydronic water that's recovering. The size of the indirect coil limits tank recovery rate.
    Ngriswold