Stuck MoM (and maybe Gorton) Vent Mystery Solved?
Chris_L
Chris_L Member Posts: 354
I recently opened up a brand new MoM vent that I had received a some years ago, which was stuck closed. I found this:
For Gorton vents, some have attributed the same problem--the pin out of the bimetal strip--to mishandling. But once I fixed this Mom vent, I couldn't get the pin to come out no matter how hard I shook it.
So I did a simple experiment and found it didn't need any mishandling at all for the pin to come out. It just needed cold.
I gently put the fixed vent in my freezer--back side down--to see how loose it got when cold. Here is what I found when I took it out:
The same thing. The pin came out of the strip while it sat there with no shaking at all and the vent is now stuck closed again.
So it seems when it gets cold enough, the bimetal strip opens enough to allow the pin to fall out. This obviously isn't something that will happen in use, but it certainly could during shipment or while sitting on a truck in the winter.
@ethicalpaul, if you still have your open Gorton vent, could you try this? First turn it upside down so the vent closes. Then put it in your freezer with the open side up. See if it gets loose enough for the pin to come out of the strip.