Sputtering water at Air Vent
Mlop
Mlop Member Posts: 6
Bought a 100+ year old building and going through first heating season.  I have set about tilting radiators toward the valve and replacing air vents. It's a two story building and some of the vents spit just. A little water, and one in particular, drops of water come out. This is after letting the system run for a while.
    ethicalpaul Member Posts: 8,252
    Are the vents "steam hot" when they do this? if so, they might have failed open so they are letting steam out that is condensing
  • Mlop
    Some of the air vents ,after firing dry air comes out and then they shut off, but after a time, steam comes out. I noticed a strange almost like raining sound in some of the radiators.  The sight glass is dirty and the water seems to bounce.
  • neilc
    neilc Member Posts: 3,139
    what's the boiler pressure when spitting?
    service your pigtail at all ?
    pictures from the basement please
    known to beat dead horses
  • Waher
    Waher Member Posts: 368
    What's the pressuretrol setting? Is the pigtail to the pressuretrol clear? Are the main air vents on the mains working? It's possible that the system is building too much pressure and eventually the vents on the radiators are leaking steam from excessive pressure.
  • Mlop
    edited January 2024
    Picture taken while running for a while.
  • Mlop
    I have found about 5 vents in the basement, two closest to boiler, and three in a different segment, one of those three fills with water and drips after a while. Pressuritol set to around 7 psi.
  • neilc
    your Ptrol on the left is a high limit, manual reset, last chance safety,
    the red button is the reset,
    you don't have to reset that at all, do you?
    The Ptrol on the right is the operating pressure, it looks to be set ~ correct, as low as can be,
    inside, under that cover is a wheel, 1-5, it should be set to 1,
    the gage shows about 2 psi, if it gets higher than that then you're having issues,
    has the pigtail been serviced?
    you should be able to blow thru it, all the way back into the boiler with minimal resistance,
    so the Ptrols and gage can see what's happening in the boiler,
    Have you serviced that pigtail?
    can we see a picture of the 3 vents?
  • neilc
    and post a general view of the boiler and the sightglass, floor to ceiling,
    do you have and have you skimmed?
  • Mlop
    Thank you all for the guidance, I've seen some these terms mentioned in previous posts, this is new to me, I'll get some pictures as soon I can make it over there. I haven skimmed it, and is the pigtail the well I guess pigtail looking pipe? I've only had the building since July or so.
  • neilc
    yes, pigtail looks like one,
    it is a water trap to protect the Ptrol against hot steam,
    they tend to clog up with boiler gunk,
  • Mlop
    Steamhead Member Posts: 18,280
    I looked at the manual for your boiler. The piping connecting the boiler to the system is completely wrong. The steam outlets are 4-inch, but someone reduced them to 2-inch. This is probably allowing water to get up out of the boiler into the system, where it reduces efficiency and causes spitting vents and probably banging.
    Where are you located? We might know someone who can help you.