Why does my zone valve use 40v transformer?
drosner
drosner Member Posts: 65
I’m replacing my taco circulator zone control and I have one zone where a prior owner/contractor put a zone valve along with a zone circulator. I’m pretty sure they did that to prevent flow when that zone isn’t on. Either way it works just fine.
Here’s my question…I see they added a 40v transformer and in reading the Taco 571 docs it also indicates to use a 40v transformer. However the specs of the 571 say it’s a 24v device. Why does Taco say to use a 40v transformer to power a 24v valve?
    mattmia2 Member Posts: 16,076
    edited January 2024
    Pretty sure it is 40va 24vac(nominal). 40 va is the power it can provide and is equivalent to a watt but accounts for power factor.
    STEVEusaPA
  • va stands for volt amp
    vac stands for volts alternating current
  • drosner
    Uh thank you for clarifying and I feel pretty stupid right now!
    hot_rod Member Posts: 27,110
    24V X a .9 Amp zone valve = 21.6 Va
    Don’t bother. We all have a lot to learn.