Why does my zone valve use 40v transformer?
drosner
Member Posts: 45
I’m replacing my taco circulator zone control and I have one zone where a prior owner/contractor put a zone valve along with a zone circulator. I’m pretty sure they did that to prevent flow when that zone isn’t on. Either way it works just fine.
Here’s my question…I see they added a 40v transformer and in reading the Taco 571 docs it also indicates to use a 40v transformer. However the specs of the 571 say it’s a 24v device. Why does Taco say to use a 40v transformer to power a 24v valve?
Here’s my question…I see they added a 40v transformer and in reading the Taco 571 docs it also indicates to use a 40v transformer. However the specs of the 571 say it’s a 24v device. Why does Taco say to use a 40v transformer to power a 24v valve?
0
Comments
-
-
va stands for volt amp
vac stands for volts alternating current8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Uh thank you for clarifying and I feel pretty stupid right now!0
-
24V X a .9 Amp zone valve = 21.6 VaBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
drosner said:Uh thank you for clarifying and I feel pretty stupid right now!8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements