Help wiring stat to rib relay to control fan on CUH
fedupwithcontrols
Member Posts: 7
Ok, dumb plumber here who hates wiring. I have a Noble combi boiler with a Taco 3 zone relay controller. I’m trying to use heat only Rodgers-White stat to turn on the fan on the CUH and the circulator pump. I bought a RIBU1C relay to hopefully power up the fan. I also have a 24v knock down transformer somehow that needs to power up the stat too. I have a 5 wire stat line running from stat to CUH where the relay and transformer are. From there to the Taco controller I have another 5 wire running. Does anyone have a dumbed down drawing I can follow? I’m ready to throw stuff. 😂
Is the Taco 3 zone relay controller a pump control or a zone valve control?
SR503 is a pump control.
ZVC503 is a zone valve control.
The wiring is different on each.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Where is all this stuff physically located? Is the circ in the boiler room and fan at the CUH? A common way to do this is to wire the circ to the Taco relay and then have the fan run off a strap-on aquastat or snap disk strapped to the supply pipe at the heater. This way the fan never blows cold air. As soon as the pipe heats up the fan turns on..."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Fed up it’s cool, you can prolly run circles around us with other things trade related
I know that RIB control, and general low-voltage pretty well. I do not have one in my hand, so I cannot cite the colors.The RIB has two things going on-
the coil
the relay or contactor
I cannot fully understand, you have an air handler? I can’t place what CUH is at the moment
Does the fan coil have fan center? What terminals make the fan come on?And tell me the purpose of the Taco0 -
On the RIB
orange NO, blue NC and yellow (common) are the relay contacts. On the coil white/yellow is common, white/black is 120 volt and white/blue is 24 volt0 -
Hello @fedupwithcontrols,
With the information provided, if the Taco does not control the circulator for the fan unit, I would do it this way.
One Pipe System0 -
@fedupwithcontrols Are you there?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Sorry for the delay fellas. I’m using the Taco sr-503. Circ is in boiler room. CUH is upstairs. Pic is a drawing of all the components I have in this puzzle.
What is a CUH (Central Unit Heater?) and is there a wiring diagram for it?
What are B and W for the CUH?0 -
I do no fully understand the CUH. I realize it is an air handler with a blower and a hot water coil. Is there also a coil for cooling?
Your diagram shows the only wire connections to the CUH is B and W. Is that the only wiring? Is there a place to connect the thermostat, or is it just the B for Hot and W for Neutral to the blower motor?
If that is the case then you have the incorrect RIB relay. You need RIB2401D (See Below) so you can turn on the blower and the low voltage to the zone control. I believe that RWC is where the thermostat would go for that zone on the Taco 503, but you need to verify that.
If you do not want the CHU to blow cold air during the time it takes to get the hot boiler water from the basement to the attic, you will also need to purchase a FAN thermostat like the adjustable L6006C from Honeywell or a Snap Disk to place on the return pipe in the attic. This will keep the blower off until the coil is hot.
https://www.supplyhouse.com/Functional-Devices-RIB2401D-Enclosed-Pilot-Relay-10-Amp-DPDT-w-24-VAC-DC-120-VAC-Coil?_br_psugg_q=rib+relay
https://www.supplyhouse.com/Resideo-L6006C1018-High-or-Low-Limit-Circulator-Strap-On-Aquastat-65-200-DegreeF-range-5-30-DegreeF-Adj-Differential
OR
https://www.supplyhouse.com/White-Rodgers-3F01-130-3-4-Snap-Disc-Fan-Control-Cut-In-130-Degrees-F-Cut-Out-115-Degrees-F
Here is the diagram, unless the CHU has a wiring diagram that has other components already in there. Also is the CHU also doing cooling?
If the Taco SR-503 will be controlling the circulator then this should work. Transformer phasing should be checked. If you don't want to deal with the transformer phasing you would need a DPDT (like RID2401D) type relay to provide an extra set of isolated contacts for the Taco SR-503 control.
One Pipe System0 -
IMPORTANT
I just thought of something. The CHU may have a 220/240 Volt blower motor, so it is important to connect a 230 VAC input transformer in that case. Check the blower motor rating and measure the voltage with a meter. The 24 VAC transformer MUST have a matching primary (input) voltage for this diagram to workEdward Young Retired
Hello @SuperTech,
In this case I suspect it is something like this.
http://www.2hsc.com/airtex/PDF/CUH_Series.pdf
One Pipe System0 -
109A_5 said:Hello @SuperTech, In this case I suspect it is something like this. http://www.2hsc.com/airtex/PDF/CUH_Series.pdf
I think if the OP wants to move forward, he or she can provide the wiring diagram for their particular unit. Or at least a make and model. Throw us a bone, ya know?0 -
Hello @HVACNUT,
I'm assuming it is just a blower motor B & W (Hot & Neutral). It would be nice if there was a water temperature switch (aquastat) in the cabinet too, but probably not. Yes, more information may help.HVACNUT said:Nice, but it doesn't show wiring.
Also no C wire included on the device / wire color / connection terminals note.fedupwithcontrols said:I also have a 24v knock down transformer somehow that needs to power up the stat too.
One Pipe System0 -
On the Aquastat, is that line voltage or low voltage i would wire up? Also someone asked about the heat only stat, it has a R and W terminal. Below is the stat.
https://www.supplyhouse.com/Robertshaw-RS1100-72-1H-Programmable-Thermostat-w-72F-Max
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 111 Geothermal
- 163 Indoor-Air Quality
- 72 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
