I have to manually power cycle air handler to get zone to provide heat
dhoskyns
Member Posts: 3
2-zone AC/hydronic heat system:
2- Zone system AC / Hydronic heat
Buderus boiler
Taco SR-502 relay
ADP Air handlers
Zone 2- works perfectly
Zone 1 - A/C works and manual fan control works. But when I call for heat on my thermostat nothing happens - No red zone 1 light on Taco relay, circ pump doesn't run and air handler doesn't blow. HOWEVER if I flip the power switch on the side of the air handler off/on and wait 5 seconds, the red zone 1 light comes on on the Taco, circ pump and air handler turn on and I get heat. This works every time...Issue happens 2-3 times a day.....does anyone have any idea what the issue is? I have already replaced the thermostat. Is the the Taco relay bad or possibly the 24v relay inside the Taco? Any thoughts appreciated.
Buderus boiler
Taco SR-502 relay
ADP Air handlers
Much more likely to be a problem with a switch in the air handler than something with the Taco. Figure out how the air handler tells the Taco to turn on, and trouble shoot from there.Br. Jamie, osb
Thanks Jamie. I will start with the air handler. Not too much inside to troubleshoot..
Can you turn the fan to constant "on" at the thermostat will the thermostat start the heat? This could get you going until you can troubleshoot. It could very well be the sequencer as @HVACNUT mentioned.1
Yes, the red and white wires go to the Taco.....ordering a new sequencer.
Thanks @HVACNUT and @EBEBRATT-Ed0
- 169 Indoor-Air Quality
- 50 Industry Classes
go to the Taco relay? If so it's probably faulty contacts in the sequencer. Get the numbers off it and order a new one.