Uponor heating not working
Calum94
Member Posts: 4
Uponor is cold across all zones. Fully reset the system and synced the thermostats and all zones are asking for heating.
The inlet pipes from the boiler are warm and the upstairs radiators are working.
The manifold past the pipework however is cold, though the flow rates to each zone under power are functioning correctly so don’t think it’s the actuators (concurrent failures of all zones seems incredibly unlikely)
Out of ideas and everyone is closed for the festive period!
The temperature gauges by the Wilo pump, what do they read. Looks like you have flow in every loop, so you need to confirm the boiler is firing.Bob "hot rod" Rohr
It’s reading 15c on the gauge, realised the heating is now not reaching the manifold so must have only been warm initially due to the boiler running the radiators upstairs?
Moved some plastic from under the pump and think I might have a small leak from what I can only guess is the return line? (Under the foam pictured)
though the hot water should still be running still?
so it appears the system is not asking for heat from the boiler like previously thought so out of ideas!
Small update, appears that end of what I’m guessing is the blending unit (wire from thermostatic head goes into) was loose and damp. Not sure why that would take the heating out given it’s just not asking the boiler for heat
Might have cracked it!!!
actuator might have failed closed in auto wrenched it over to manual with some resistance and the systems come back, manifold and plastic pipes now warming up
Any issues running in manual?
Do you have a wiring schematic?
Typically thermostats open the blue actuators, & maybe that silver valve. Then those actuators call the boiler and pump on.
If the silver valve turned on the pump and boiler when you manually opned it, check for power to that control.
But you need to know the control logic that someone wired.Bob "hot rod" Rohr
Those actuators often have an end switch that once it is open will call the boiler on, if that is what is calling for heat then leaving it in manual will make it so that the boiler is always on. I would use this opportunity to maybe clean up that control scheme a bit though, looks like you have a zone valve, a TRV, and loop actuators all controlling the same thing which could be done with only the loop actuators.0
- 15.8K Strictly Steam