WM combi heat exchanger bad in 3 years
ChrisJ
ChrisJ Member Posts: 17,350
My sister's WM combi unit needs a heat exchanger and I think it's only 3 years old.
I'm assuming this isn't normal, is there anything typical that causes such a failure this fast that I mention to her?
Unit runs on LPG and they have well water. Unfortunately I don't know much more than this at this point.
    hot_rod Member Posts: 27,413
    Is it leaking? If so where?
    Water quality
    Inadequate flow
    Combustion not dialed in
    ChrisJSuperTech
  • ChrisJ
    edited December 2023
    Water quality
    Inadequate flow
    I doubt it's leaking, but how do these work with domestic hot water? That's fresh water being fed into it somewhere?
    The other 3..........I wouldn't be surprised if all 3 are issues.
    EDIT : I just realized you meant is the heat exchanger leaking. I'll ask.
    EBEBRATT-Ed Member Posts: 20,145
    If it was installed right it should last 3 years if you do nothing to it. Unless something unforeseen happened to it.
    ChrisJ
    ChrisJ said:
    Water quality
    Inadequate flow
    I was thinking in terms of the boiler (HX). Is it the flat plate HX for DHW that is leaking?
    Most brazed plate type, O ring connections into a composite block, one or two pinch bolt keeping it together.
    ChrisJ
  • ChrisJ
    I'm told the return tube to the heat exchanger is leaking at a factory connection where's it's crimped.
    Their contractor is working with WM to try and get it replaced
    It sounds like it's caused damage to a board as well
  • HomerJSmith
    HomerJSmith Member Posts: 2,774
    Have your well water tested. Well water can have a lot of minerals in it. That can plug up the heat exchanger.
    ChrisJ
  • kcopp
    kcopp Member Posts: 4,669
    Is this the Aqua balance?
    ChrisJ
  • ChrisJ
    Yessir
    She just sent me this