Weil CGt diverter
kcopp
Member Posts: 4,669
I service 2 Weil Mclain CGt boilers.
Both are having issues w/ the heat staying on even if the Thermostats are not calling for heat. I even pulled the wires off the boiler and they would still circulate water.
Sometimes cycling the power gets the issue to reset.
Would a diverter valve sticking cause this to happen? I cant believe this is electrical...especially w/ two boilers.
tia
tia
Do they have zone valves connected? What wires did you pull off? Is there an outdoor reset control connected?Bob "hot rod" Rohr
1 zone.
Pulled the tt off the boiler / end switch .
Simple cast iron block w a coil inside.
Side wall vent in stainless.
No outdoor sensor.
So the issue turns out is a sticking diverter valve.
Its not electrical in any way....
The piston inside the 3 way valve has very tight tolerances. There is sone Non-Barrier tubing in the system.
Strange thing is that is sticks every so often and when it does it stays in heat mode.
Very odd...
I have done a power flush, replaced the piston and added an inhibitor.
fingers crossed.