Weil CGt diverter

kcopp
Member Posts: 4,517
I service 2 Weil Mclain CGt boilers.
Both are having issues w/ the heat staying on even if the Thermostats are not calling for heat. I even pulled the wires off the boiler and they would still circulate water.
Sometimes cycling the power gets the issue to reset.
Would a diverter valve sticking cause this to happen? I cant believe this is electrical...especially w/ two boilers.
tia
Both are having issues w/ the heat staying on even if the Thermostats are not calling for heat. I even pulled the wires off the boiler and they would still circulate water.
Sometimes cycling the power gets the issue to reset.
Would a diverter valve sticking cause this to happen? I cant believe this is electrical...especially w/ two boilers.
tia
0
Comments
-
Do they have zone valves connected? What wires did you pull off? Is there an outdoor reset control connected?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
1 zone.
Pulled the tt off the boiler / end switch .
Simple cast iron block w a coil inside.
Side wall vent in stainless.
No outdoor sensor.
0 -
So the issue turns out is a sticking diverter valve.
Its not electrical in any way....
The piston inside the 3 way valve has very tight tolerances. There is sone Non-Barrier tubing in the system.
Strange thing is that is sticks every so often and when it does it stays in heat mode.
Very odd...
I have done a power flush, replaced the piston and added an inhibitor.
fingers crossed.
0 -
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements