Expansion tanks, trapped air
CBRob
Member Posts: 291
I think all of these tanks are allowed to be installed vertical. How would the trapped air ever get out?
With a bladder tank there is always air on one side of the bladder and boiler water on the other side. The expansion tank acts as an air cushion to keep the correct pressure in the system.
Wit a bladder tan you need automatic air vents or manual air vents or a air scoop or microbubble eliminator to remove the air from the system.0 -
Wouldn't air be trapped under the bladder when the threaded end is down?
I've always installed them threads up.0 -
thread up is preferred, thread down or horizontal are acceptable, according to Zilmet instructions.Bob "hot rod" Rohr
Living the hydronic dream0