System 2000 EK2
I have an EK2 installed in 2009. It recently started kettling pretty bad when it gets up to temperature - very loud banging and then the pressure relief blows. I ran boiler cleaner through it and drained 3 times to hopefully handle any scale. There was no change in the kettling. The temperature gauge is quite high but I'm not sure if that's normal. I replaced the T&P valve with a new one so I'm pretty sure that's good. Do the return water sensors ever go bad? Is it the energy manager? It's cold now here in Alaska and I don't want the house to freeze.
    Steamhead Member Posts: 18,498
    @Roger ?
    Consulting
  • bburd
    bburd Member Posts: 1,303
    If the pressure relief blows repeatedly, that suggests that the expansion tank has failed.
    Bburd
  • Roger
    Roger Member Posts: 472
    Thank you for your post, @akgrizzlylodge , and for your suggestion @bburd .  Based on the description, I’d agree that it’s likely a failed expansion tank, possibly a failed circulator as well.
    Roger
    President
    Energy Kinetics, Inc.
  • Roger
    I should have mentioned that it should not kettle, either. It likely needs a more thorough cleaning. A heating pro can call us to get those instructions.
    Roger
    President