Two Water Heaters Break Back to Back
dimo
Member Posts: 7
We recently purchased our house. About a week after moving in our water heater went out. It threw out a code of “failure to ignite”. The water heater was 10 years old so we figured that was the problem and purchased a new one which was professionally installed. Two months later our brand new water heater went out and is throwing out the same code.
The water heater is propane powered and our other propane appliances don’t seem to be having an issue. What could be causing this issue?
What make and model heater?All Steamed Up, Inc.
Consulting0 -
The current one is a reliance 606. The old one was a Lochinvar with a Honeywell electric igniter0
where is the water heater located in relation to the other appliances? are others using the same chimney?0
It has its own chimney and it has a blower on it. It has its own “closet” and the only thing around it is our water filtration system. Our propane powered furnace is in the crawl space and our dryer is down the hall from it.0
Has anyone actually checked the gas pressure when the water heater is running -- or trying to? What size and length is the gas line?Br. Jamie, osb
when you say blower do you mean on the top of the water heater (power vent) or a draft inducer cut into the flue?0
Jamie Hall said:Has anyone actually checked the gas pressure when the water heater is running -- or trying to? What size and length is the gas line?0
A blocked vent?Bob "hot rod" Rohr
into the chimney? did you bring the pvc/cpvc flue all the way out thru the roof. you can only use the chimney as a chase and it has to be the only applance in the chimney. you cant pressurize a chimney0
pedmec said:into the chimney? did you bring the pvc/cpvc flue all the way out thru the roof. you can only use the chimney as a chase and it has to be the only applance in the chimney. you cant pressurize a chimney0
OK. how big is the room that the water heater is in? and just to clarify you only have one pipe and it's an exhaust.0
Could be a bad ground.
Could be gas pressure.
Could be the flame sensor.
Could be condensation dripping on the burner.
Only one way to find out for sure.
What I'm thinking is if I have two similar items -- in this case water heaters -- and they both fail in a similar way fairly close together, they are very likely not the problem. Something common to them is.Br. Jamie, osb
If the exhaust stack is not set up with a double elbow to protect the exhaust flow that may be an issue just as spider webs and bird nests can be in a standard chimney.
If the door is closed in this "closet" you have a very small amount of square area available that will allow air for combustion to enter the firebox of the water heater.
You may need to install an air vent grid in the bottom of the door to allow enough combustion air into this "closet". Your installer should have told you this to begin with.
When checking with the Reliance website model 606 keeps coming back as an electric hot water heater. To identify better, we need the model number. Some power vented water feeders rely on ambient air (room air) for combustion. Possibly when the door to the closet is closed, there isn't enough air for proper combustion and It fails to ignite.1
- 87K THE MAIN WALL
- 114 Chimneys & Flues
- 106 Geothermal
- 981 Plumbing
- 388 Solar