Weil mclain pilot/ ignitor assembly
Options
jc2lite1
Member Posts: 18
I have a weil mclain EG-50-PI series 2 steam boiler installed in 1998. The pilot light would not light. Wire was bad. I purchased a new assembly and the pilot fires tight up but no burners. Contacted Weil mclain and they tell me it will not work with the old gas assembly and I need to purchase a conversion kit for over $700. My question is, is there a way to hook up the thermocouple wire to the old version to make it work? TIA.
Weil McLain EG-50-PI 175000 2 pipe Steam Boiler Vacuum System. Installed 12/13/91..
0
Comments
-
-
That's probably the old White-Rodgers system that used the mercury flame sensor. The end of the sensor looks like a thermocouple but it's not. We typically upgrade these with Honeywell Y8610U kits, and yes, they are not cheap, but are fixable using standard parts.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Sorry guys, I did not see your comments. I was able to find a replacement on Ebay and up and running.
Weil McLain EG-50-PI 175000 2 pipe Steam Boiler Vacuum System. Installed 12/13/91..
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 169 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements