Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Weil mclain pilot/ ignitor assembly

I have a weil mclain EG-50-PI series 2 steam boiler installed in 1998. The pilot light would not light. Wire was bad. I purchased a new assembly and the pilot fires tight up but no burners. Contacted Weil mclain and they tell me it will not work with the old gas assembly and I need to purchase a conversion kit for over $700. My question is, is there a way to hook up the thermocouple wire to the old version to make it work? TIA.
Weil McLain EG-50-PI 175000 2 pipe Steam Boiler System. 33+ years old.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,474
    Need pictures and model #s of what you have
    mattmia2
  • Steamhead
    Steamhead Member Posts: 17,380
    That's probably the old White-Rodgers system that used the mercury flame sensor. The end of the sensor looks like a thermocouple but it's not. We typically upgrade these with Honeywell Y8610U kits, and yes, they are not cheap, but are fixable using standard parts.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2