Is this a NEW Weil McLain EG50 or this is a bait and switch?
I've only seen 1 new block in person and it was my EG series.
But that to me certainly looks like a new EG50 or EG55 (same block).
The surface rust doesn't mean anything.
Okay thanks, that does calm my nerves a bit.ChrisJ said:I've only seen 1 new block in person and it was my EG series. But that to me certainly looks like a new EG50 or EG55 (same block). The surface rust doesn't mean anything.0 -
Altoiditis said:ChrisJ said:I've only seen 1 new block in person and it was my EG series.
If you're having a steamer put in and want to clarify the piping etc with us before it's done, please by all means. It's easier to have it done right the first time than to try and get it fixed.
But I think your new block is the real deal.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Hopefully it was sized correctly already. Judging by the return pipe that's already perfectly lined up with the return connection, I have some doubts. I guess this website has made me paranoid.ChrisJ said:Altoiditis said:ChrisJ said:I've only seen 1 new block in person and it was my EG series.
To the OP, sizing and proper piping are way more important than that surface rust, which isn't uncommon on bare cast iron.0 -
Please see above for previous one’s piping, it’ll be the same unless there was something wrong with the previous.KC_Jones said:ChrisJ said:In terms of sizing, it’s 175k BTU, it’ll be steam. I’ve done rough math with the radiators around the house and main pipe and based on that it says I need 350 Sqft ratings, this unit is 454 sqft, however I do plan to finish the basement and add heating to it from this unit. It’s a 2100 Sqft brick facade house.0 -
Assuming that's 2" pipe (not outside diameter, that's more like 2 3/8") then it's piped to minimum specs.
If it was mine, I'd want that piping all upgraded to 3" but according to Weil Mclain it's fine the way it is unless I missed something.
Even with finishing your basement I wouldn't have gone over an EG45.
I'm running an EG-40 with 392 sqft.
But, you're passed that point.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
2 -
Riser and header should be minimum 2 1/2" pipe which is 2 7/8" OD, I can't tell what that is so as long as it's 2 1/2" pipe it's ok. I agree with Chris I'd prefer full size 3" outlet and header.
As far as the sizing, that ship has set sail, but yeah it's oversized, dramatically regardless of what you are doing with the basement.
I will never understand doing the math and then ignoring it, never understand. the 45 would have been better, but I'm betting the 40 would have worked just fine with 22% pick up factor.
As it stands you have 70% pick up factor, which is absolute insanity.
@KC_Jones That's interesting.
I remeber the chart you posted, that's the one I used.
But here's a more recent one and apparently they've reduced their recommendations.
No idea why so I can't really comment on that but if it was mine I'd still do a single 3" into a 3" header.
The screenshot I posted was off their website, just today, so I don't think it's outdated. Perhaps the one you saw was an older typo? The one you posted actually disagrees with itself.ChrisJ said:@KC_Jones That's interesting.
Looks like the one that lists a single 2" is a typo, looks like it should say one 2.5" or two 2" risers, otherwise why would there be a 2" and a 2.5" minimum line for the same boiler group.0
Certainly looks like a five section Weil Mclain boiler. Every single new boiler has rust like that. Probably spilled cutting oil or something like that.0
I think the rust is from them pressure testing the boiler with it full of water. That would be safer than testing it with air.
3