Distance between fittings and circulator
Orangecoleahh
Member Posts: 1
in Oil Heating
Is there a minimum distance between say a 90 and a circulator, on a oil fired boiler?
Best practice is 12D, 12 pipe diameters up or down stream. So 12" for 1" pipe or tube.
No flow restricting devices up stream of a circulator. Air separators are fine upstream.
But even pump manufacturers break this practice by putting check valves in the discharge of the volute. Go figure.Bob "hot rod" Rohr
Living the hydronic dream1 -
If space is a concern, I’d pay more attention to the suction side of the pump, i.e. 10 diameters of straight pipe.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
12D, 12 pipe diameters, so for 1” pipe or tube 12” is best practice on both sides of a circ
no check valve or flow restrictive devices at the suction
But even the pump manufacturer break this rule with IFC checks in the pumpsBob "hot rod" Rohr
@Orangecoleahh I've merged your duplicate posts into one here to prevent confusion. Thanks.
President
HeatingHelp.com0 -
Hi @Erin Holohan Haskell
there may be a glitch in the interwebs,
This is a second "merge" where I only see about 5 messages of this thread,(happened on another where I tagged you on the duplicate threads),
Where is all the starting messages to this thread?known to beat dead horses0 -
@neilc, I usually merge the posts and then remove anything that is duplicate, like the OP's initial question repeating. I'll keep an eye out for glitches. Thanks!
President
HeatingHelp.com0 -
- 116 Geothermal
- 169 Indoor-Air Quality
