Max supply water temperatures for radiant.
mburg
Member Posts: 48
What would be the highest water supply temperature for radiant in a concrete slab, or gypcrete?
On a well designed system, 130°F.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
maxxon states that its gyp products resists breakdown up to 150F
Why do you ask? That would be a very high temperature on a floor, even with a covering over itBob "hot rod" Rohr
I understand that you should never design a system that requires that high of a supply temperature, but could there be any damage to the tubing, or concrete if higher water temperatures are used?Is there any concern if 180 degree water goes into a gypcrete or concrete system at startup for a bit.I am replacing a condensing boiler that feeds 14 space heating zones and a 120 gallon indirect. There is currently mixing valves for all 14 space heating zones. I was considering removing all of them and allowing outdoor reset to set a supply temperature for all zones. (Except garage and basement. I will leave mixing valves on those zones) Some of the valves are leaking and it seems like a good way to get a bit more efficiency out of the system.My concern is after a domestic hot water call the boilers, near boiler piping, low loss header, etc will be up to 180 degrees. Depending on how many zones are calling after a domestic call it could take several minutes or more to cool the water to a more appropriate temperature.Would this be a bad idea?0
A small, short slug of 180F water into the radiant will not be a problem. I doubt it would last a few minutes and would dissipate quickly.
Does your system control have a post purge setting? You could dump that higher temperature into the indirect. Most relay boxes and boilers have post purge for one circulator.Bob "hot rod" Rohr
Living the hydronic dream1 -
That’s a good idea.Thanks for the input.0
- 121 Chimneys & Flues