Max supply water temperatures for radiant.
mburg
Member Posts: 46
What would be the highest water supply temperature for radiant in a concrete slab, or gypcrete?
0
Comments
-
On a well designed system, 130°F.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
maxxon states that its gyp products resists breakdown up to 150F
Why do you ask? That would be a very high temperature on a floor, even with a covering over itBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I understand that you should never design a system that requires that high of a supply temperature, but could there be any damage to the tubing, or concrete if higher water temperatures are used?Is there any concern if 180 degree water goes into a gypcrete or concrete system at startup for a bit.I am replacing a condensing boiler that feeds 14 space heating zones and a 120 gallon indirect. There is currently mixing valves for all 14 space heating zones. I was considering removing all of them and allowing outdoor reset to set a supply temperature for all zones. (Except garage and basement. I will leave mixing valves on those zones) Some of the valves are leaking and it seems like a good way to get a bit more efficiency out of the system.My concern is after a domestic hot water call the boilers, near boiler piping, low loss header, etc will be up to 180 degrees. Depending on how many zones are calling after a domestic call it could take several minutes or more to cool the water to a more appropriate temperature.Would this be a bad idea?0
-
A small, short slug of 180F water into the radiant will not be a problem. I doubt it would last a few minutes and would dissipate quickly.
Does your system control have a post purge setting? You could dump that higher temperature into the indirect. Most relay boxes and boilers have post purge for one circulator.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
That’s a good idea.Thanks for the input.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements