Wiring for ra117a stack relay
daveanna
daveanna Member Posts: 1
I'm replacing my original stack relay with the updated replacement part ra117a.but I'm not exactly sure how to connect the wiring inside. I can't get 24 volts to the TT wires to the thermostat and it's not working at all. HELP!!!
    Jamie Hall Member Posts: 27,376
    T-T is not looking for 24 volts. All it cares about is whether it is seeing an open circuit (burner off) or a closed circuit (burner on).
  • STEVEusaPA
    That primary control is outdated 1940's technology (and expensive). It should be replaced with something modern.
    HVACNUTSuperTech
    HVACNUT Member Posts: 7,451
    It's 2023. Why on earth are you STILL using a stack primary? Is it because the burner is just as old?
    Do the thermostat wires go the stack relay or to a different relay? TT is usually jumped in the primary but don't do that if you're not sure.
    Is the helix in step? (I can't believe I remembered that. But don't ask me what I had for breakfast.)
    STEVEusaPA
    Steamhead Member Posts: 18,500
    This. @daveanna , can you post some pics of the unit this is mounted on? Also, where are you located?
    Consulting
    EBEBRATT-Ed Member Posts: 20,185
    I like old stuff but it's long past the time to get rid of any stack switch
    120 volt power (after you go through all limit controls goes to terminal 1 (hot) and terminal 2 (neutral). Terminal 3 goes to burner motor. Terminal 4 goes to ignition transformer.
    Sometimes you will find the burner motor and ignition transformer both on terminal 3.
    Thermostat terminals are r-Red, w-white and B blue for a three wire thermostat.
    For a two wire stat use r & w
    BUT YOU NEED TO GET RID OF THAT CONTROL WITH IT'S 90 SECOND SAFETY TIMING IT IS FAR OUTDATED.
    If your unsure what to do get some professional help.
    And oil or gas burner can cause serious problems if not properly installed and serviced