A.O smith water heater issue.
nytech28
Member Posts: 99
I have domestic hot water heater , it ignites but no flame all other safetys are good , can this be a thermostat issue ? also I would like to attach few pictures of the job , & would aprecaite if I am explained how the plumbing is connected & cause of the no flame , plz update 





0
Comments
-
Hi, Does the vent fan ever run?
Tours, Larry0 -
yes the fan does run , air flow switch is closed & high limit switch0
-
Hi, It is sounding like the gas control to me, but have you contacted AO Smith and/or White Rodgers? Maybe they have some clues 😏
Yours, Larry0 -
On your list of to-dos
It looks like the circulator pump in the pic is mounted upside down?
This water heater is running a hydronic system?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
it's the gas valve & I have contacted A.O smith already.Larry Weingarten said:Hi, It is sounding like the gas control to me, but have you contacted AO Smith and/or White Rodgers? Maybe they have some clues 😏 Yours, Larry
0 -
to my understanding so far it's just being used as demostic hot water , as for the plumbing side of the system I will draw a diagram & attach & suggestion would be apreciated.
hot_rod said:On your list of to-dos
It looks like the circulator pump in the pic is mounted upside down?
This water heater is running a hydronic system?0 -
This pump here is mounted upside down. It looks to be cast iron and the flanges also. If it is the hot water recirc it should all be brass or stainless.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
update I got the hot water running , issue was the thermostat/ gas vavle . thanks for looking into this0
-
Hi @nytech28 , Good you got it running. What was the issue with the gas valve? Field serviceable? Thanks!
Yours, Larry0 -
the gas valve was defective , no error codes or response , don't think it was field serviceable I just installed new vavle & kidos in class is getting hot water on there bathroom.Larry Weingarten said:Hi @nytech28 , Good you got it running. What was the issue with the gas valve? Field serviceable? Thanks! Yours, Larry1
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 117 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.7K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements