No external pump output
Bob6
Member Posts: 5
in Gas Heating
We have a 2 year old Rheem Prestige combi boiler. Yesterday the output to the external circulation pump stopped working. The panel screen shows that the pump is to be turned on but zero voltage at the terminals. The rest of the system is working fine, no blown fuses, power transformer is fine, just no voltage the the zone pump. I ordered a replacement circuit board, but don't see any components on it like a relay that would be used to turn on a pump. Any ideas?
Thanks
Thanks
Hello @Bob6,
No model number so this is a just guess as to the manual. Looks like there are relays or maybe they are actually Triacs (a solid state AC switch). Failed solder joint ? Pin fitment at a connector ?
One Pipe System0 -
Hello. I completely missed that schematic in the manual. It's a Rheem Prestige model RCBH199DVLP. The schematic you posted looks to be correct. I'll take a look at the solder joints. Has to be something simple. It has been running fine for 2 years and zip, no external pump.
Thanks for your help,
Bob0 -
@Bob6
You might check the pump motor to see if it is ok. Disconnect it and temp wire it to a source of power. You don't want to smoke a new circuit board due to a defective pump.0 -
Already did that. Motor is fine. To be on the safe side I'm going to add in a 1 amp inline fuse into the pump wiring before I swap out the board when it comes. The unit is limited to 2 amp pump max. The pump is .71 amps. Fuses are cheap, boards not so much. Personally I think your thoughts on bad solder joint is probably the most logical cause. Seen that before on circuit boards on various cars I've owned in the past.0
Before you swap out the boards, check all the connections -- particularly plugs and sockets. You doubtless know that anyway, since you mention cars... I'd say that 90% of the failures on modern cars are bad power, bad grounds, or crusty sockets and plugs.Br. Jamie, osb
Will do.0
Thanks everyone. It's really helpful getting feedback from others. Most people nowadays don't know jack on equipment and your comments have helped a lot. Hope I can return the favor in the future.0
- 15.8K Strictly Steam