Oil Fired Boiler Tune Up
Albie
Member Posts: 18
Hello,
I recently had a tune up on my boiler, 4yr old Peerless WBV-03 w/Beckett burner. Technician noted without explanation that there was "draft excess air pressure". Can anyone explain what this means and if there are any negative consequences? I'm wondering if the chimney is blocked in some way.
Thank you.
Thank you.
What draft level did they measure and record? Might look something like -04 .All Steamed Up, Inc.
Consulting0 -
Here's the report:
Fueloil #2
CO2 max 15.7%
4.6% O2
36ppm CO
500 deg F Fluegas Temp
83.1% EFF
77.1 deg F Ambient Temp
-0.044in H20 Draft
28.2% Excess Air Pressure
12.24% CO2
47ppm Undiluted CO
It's excess air not excess air pressure. It's the quantity of air above that needed for stoichiometric combustion. Numbers look alright, CO is slightly high but probably from servicing.Albie said:Here's the report:
Fueloil #2
CO2 max 15.7%
4.6% O2
36ppm CO
83.1% EFF
-0.044in H20 Draft
12.24% CO2
47ppm Undiluted CO
Your numbers look fine. it looks like the burner is set up properly0
Is that draft number at the breech or over the fire?
Steve - I believe the the draft number was at the breech.
Thank you all for your comments.0