I recently had a tune up on my boiler, 4yr old Peerless WBV-03 w/Beckett burner. Technician noted without explanation that there was "draft excess air pressure". Can anyone explain what this means and if there are any negative consequences? I'm wondering if the chimney is blocked in some way.
Thank you.

Comments

  • Steamhead
    Steamhead Member Posts: 16,876
    Options
    What draft level did they measure and record? Might look something like -04 .
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • HVACNUT
    HVACNUT Member Posts: 5,844
    Options
    I would reach out to the company because "draft excess air pressure" isn't a term, especially without a number next to it.
    There is excess air.
    There is excess draft.
    There is excess pressure. 
    Is there a combustion report? 
    STEVEusaPA
  • Albie
    Albie Member Posts: 9
    Options
    Here's the report:
    Fueloil #2
    CO2 max 15.7%
    4.6% O2
    36ppm CO
    500 deg F Fluegas Temp
    83.1% EFF
    77.1 deg F Ambient Temp
    -0.044in H20 Draft
    28.2% Excess Air Pressure
    12.24% CO2
    47ppm Undiluted CO



  • Robert O'Brien
    Robert O'Brien Member Posts: 3,541
    Options
    Albie said:

    Here's the report:
    Fueloil #2
    CO2 max 15.7%
    4.6% O2
    36ppm CO
    500 deg F Fluegas Temp
    83.1% EFF
    77.1 deg F Ambient Temp
    -0.044in H20 Draft
    28.2% Excess Air Pressure
    12.24% CO2
    47ppm Undiluted CO



    It's excess air not excess air pressure. It's the quantity of air above that needed for stoichiometric combustion. Numbers look alright, CO is slightly high but probably from servicing.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,576
    Options
    Your numbers look fine. it looks like the burner is set up properly
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Options
    Is that draft number at the breech or over the fire?

    There was an error rendering this rich post.

  • Albie
    Albie Member Posts: 9
    Options
    Steve - I believe the the draft number was at the breech.
    Thank you all for your comments.